[Equest-users] outside air flow during unoccupied/setback hours
Ramana Koti
ramana.koti at gmail.com
Wed Apr 25 12:53:23 PDT 2012
That worked, thanks. It took me while to figure out the schedule type was
Frac/Design but the results showed that my model was using OA during
unoccupied hours.
Ramana.
On Wed, Apr 25, 2012 at 12:12 PM, R B <slv3sat at gmail.com> wrote:
> I should have written min OA sch (at the OA tab, system level) instead of
> the min sch at the zone level. Thanks to Ramana for pointing this out.
> -Rohini
>
> On Tue, Apr 24, 2012 at 11:54 AM, R B <slv3sat at gmail.com> wrote:
>
>> I normally have a min sch specified at the zone level - 0 for unoccupied
>> hours and -999 for other hours that takes care of this comment.
>> There is an hourly report for fan coming on during night cycle flag (or
>> something similar). If you do not have the fan coming on or do not have the
>> night cycle control, you should be ok. You can also look at the hourly
>> report for OA ratio and whether fan is on/off during the unoccupied time.
>> -Rohini
>>
>>
>>
>> On Tue, Apr 24, 2012 at 11:23 AM, Ramana Koti <ramana.koti at gmail.com>wrote:
>>
>>> Dear All,
>>>
>>> One of the LEED review comments on a university building project I'm
>>> working on suggests to verify that all systems in baseline and proposed
>>> models contain zero outside air flow when fans are cycled on to meet
>>> setback temperatures during unoccupied hours.
>>>
>>> What is the best way to go about verifying this? In the 'Hourly Report
>>> Block' options under a system, I find 'Hourly summed zone OA CFM for DCV
>>> calculation (cfm)' and 'Hourly max zone OA/total flow for DCV calculation
>>> (cfm/cf/). Is one or both of these options under an hourly report, the way
>>> to go or is there a better way of doing it?
>>>
>>> Thanks,
>>> Ramana.
>>>
>>> _______________________________________________
>>> Equest-users mailing list
>>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>>> To unsubscribe from this mailing list send a blank message to
>>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>>
>>>
>>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120425/dd7df0d5/attachment-0002.htm>
More information about the Equest-users
mailing list