Ramesh
The PSZ system requires a CONTROL-ZONE if there is more than one zone 
on the system.  If one conditioned zone is not named as the 
CONTROL-ZONE then the first zone after the system definition is 
assumed to be the control zone.  A control zone cannot be unconditioned.

The fix is to enter Detailed Edit mode, change to Air Side HVAC, 
select the System and name the Control Zone - from the list, I 
selected EL1 SSW as it is the only conditioned zone on the system.

The file opens correctly but I don't believe you can switch back to 
the Wizard Mode.

At 07:35 AM 06/08/2012, ramesh buddhi wrote:
>Dear Folks
>
>I had modeled an nine storey office Building Iam getting an BDL 
>error that zone is inconsistent with definition: The reference 
>expected a definition as TYPE= Conditioned. I designed this as an 
>unconditioned. How to get rid of this error? Please kindly help me 
>on this. I had attached the files for your reference along with the 
>weather file.Thanks a lot in advance.
>
>Thanks
>Ramesh BR
>
>   New No.110 / Survey No. 151/1, Mahatma Gandhi Road
>   Thiruvanmiyur, Chennai 600041 INDIA
>   Web: www.greenevolution.in
>   Land: +91-44-4201-8369
>   Cell : +91-99406-19915

 >>
Christopher Jones, P.Eng.
Suite 1801, 1 Yonge Street
Toronto, ON M5E1W7
Tel. 416-203-7465
Fax. 416-946-1005
email cj at enersave.ca
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120806/af8eb983/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Ramesh Buddhi.rar
Type: application/octet-stream
Size: 15889 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120806/af8eb983/attachment-0002.obj>


More information about the Equest-users mailing list