[Equest-users] Refrigeration Modeling (2) - Zone Load
Chris Jones
cj at enersave.ca
Mon Aug 6 15:15:57 PDT 2012
The equest help files are a subset of the DOE2.2 Manuals. The
Dictionary explains most keywords.
http://doe2.com/download/doe-22/
The DOE2Vol pdfs are the manuals I am referring to.
At 02:34 PM 06/08/2012, you wrote:
>Chris, thanks for the help!
>
>I agree with what you are saying, the REFG-ZONE-LOAD is the load the
>space imparts on the refrigeration case, but that is also the same
>load the case imparts on the space, hence the 'free cooling'.
>
>Thanks again for confirming the negative number in this keyword!
>
>
>
>Yoni G. Pollak, PE
>(T) 770-622-2270
>
>From: Chris Jones [mailto:cj at enersave.ca]
>Sent: Monday, August 06, 2012 1:52 PM
>To: ypollak at gtp-eng.com; equest-users at lists.onebuilding.org
>Cc: equest-users at lists.onebuilding.org; Curt Hepting
>Subject: RE: [Equest-users] Refrigeration Modeling (2) - Zone Load
>
>I am rethinking my interpretation of the REFG-ZONE-LOAD - I know
>believe the manual means "the load on the case work due to heat gain
>from the adjacent space" - the larger ( larger in the negative
>direction ) the zone load, the move compressor is used. The
>reciprocal, heat loss in the space due to the coolness "spilling out
>of the cases" is not taken into account by the program. Therefore
>the larger the negative number, the more there is "heat" in the
>space and the higher the unmet cooling hours. Just a guess but if
>you fix the REFG-ZONE-LOAD and change the space temperature you
>achieve the same effect - lower the space heating temperature set
>point, the lower the unmet cooling hours. If that is the case, then
>I suspect that the space somehow sees the zone load as increase in
>heat in the space?
>
>This would indicate that there are other REFG keywords that might
>influence the heat gain to the space due to the compressor working
>harder when REFG-ZONE-LOAD is larger.
>
>
>
>At 10:33 AM 06/08/2012, Yoni Pollak wrote:
>
>Chris,
>
>You might be right about that heat ending up in the space, but that
>doesn't sound right to me. I was getting an error when REFG-AUK-KW
>was 0, so I reset it. I've actually played around with that number
>quite a bit since it seems to have a large impact on the energy
>consumption. I'll revisit it again this morning.
>
>I'm talking aboiut umnet cooling load hours. The REFG-ZONE-LOAD
>keyword seems to be directly related to my space loads but in the
>opposite way I thought. The more REFG-ZONE-LOAD, the more system
>cooling the space requires.
>
>
>
>Yoni G. Pollak, PE
>(T) 770-622-2270
>
>From: Chris Jones [ mailto:cj at enersave.ca]
>Sent: Saturday, August 04, 2012 12:15 PM
>To: <mailto:ypollak at gtp-eng.com>ypollak at gtp-eng.com;
><mailto:equest-users at lists.onebuilding.org>equest-users at lists.onebuilding.org
>Cc:
><mailto:equest-users at lists.onebuilding.org>equest-users at lists.onebuilding.org
>Subject: Re: [Equest-users] Refrigeration Modeling (2) - Zone Load
>
>There are a number of other REFG- keywords that depend on
>REFG-ZONE-LOAD. For example:
>REFG-AUK-KW - takes three entries (order corresponds to
>REFG-ZONE-LOAD) of the fractional rated capacity of lights, fans,
>anti-sweat heaters - the default is 40% of the REFG-ZONE-LOAD - I am
>not entirely sure but I believe this heat ends up in the space.
>
>Also, do you mean the unmet load hours are cooling load unmet or
>heating load unmet?
>
>
>
>At 10:21 AM 03/08/2012, Yoni Pollak wrote:
>
>Content-Type: multipart/alternative;
> boundary="----=_NextPart_000_0096_01CD7161.C28847D0"
>Content-Language: en-us
>
>Hi All,
>
>Has anyone had experience modeling refrigeration cases? I posted a
>question the other day but this one is different.
>
>So under Air-Side HVAC Zone Parameters > Refrigeration Tab, Zone
>Load (REFG-ZONE-LOAD) I entered the free cooling affect from the
>refrigeration cases to the space (as described in the key word
>help). But looking at the SIM file, this parameter is increasing my
>zone loads rather than decreasing them, and in fact is causing my
>space to have more unmet load hours. Should I apply a negative
>number to this parameter, or is this parameter not the 'free cooling' affect.
>
>
>That along with the Walkin Box Load under the Air-Side HVAC System
>Parameter. Not sure how the program is using this value.
>
>Thanks!
>
>
>
>
>Yoni G. Pollak, P.E.
>Mechanical Engineer
>
>GTP Consulting Engineers, Inc
>4197 Pleasant Hill Rd
>Suite 200
>Duluth, GA 30096
>(770) 622-2270
><mailto:ypollak at gtp-eng.com>ypollak at gtp-eng.com
>
>
>
>
>_______________________________________________
>Equest-users mailing list
><http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>
>To unsubscribe from this mailing list send a blank message to
><mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
> >>
>Christopher Jones, P.Eng.
>Suite 1801, 1 Yonge Street
>Toronto, ON M5E1W7
>Tel. 416-203-7465
>Fax. 416-946-1005
>email <mailto:cj at enersave.ca>cj at enersave.ca
>
> >>
>Christopher Jones, P.Eng.
>Suite 1801, 1 Yonge Street
>Toronto, ON M5E1W7
>Tel. 416-203-7465
>Fax. 416-946-1005
>email <mailto:cj at enersave.ca>cj at enersave.ca
>>
Christopher Jones, P.Eng.
Suite 1801, 1 Yonge Street
Toronto, ON M5E1W7
Tel. 416-203-7465
Fax. 416-946-1005
email cj at enersave.ca