Actually ASHRAE 90.1 is the reference standard not 92.1
Bruce
On 09/08/2012 07:25 PM, Bruce Easterbrook wrote:
> ASHRAE fundamentals has design information on stratification and on
> supply air throws etc. You are getting into some pretty advanced
> modelling which eQuest won't do and your customer won't pay for. Also
> remember the Cambridge sheet is done by marketers and advertisers not
> engineers. I'm sure the unit will do much of what it claims but I
> don't think this is what you want to do if you are designing an energy
> efficient building. You are going to be able to control the buildings
> air leakage with good design. What you need initially is an idea of
> how much heat the building needs and how much fresh air. A MUA unit
> is only used to temper the incoming fresh air and can be used for
> pressurization. They are not used for heating. Too much
> pressurization is a problem as well. It doesn't necessarily reduce
> ACH, maybe a little if it is set up right and there is no wind. A
> supply air fan can be configured with diffusers to give you a high
> velocity discharge which will mix the air in the building. It will,
> if the air is released high enough also entrain some of the hot
> stratified air at the ceiling and bring it down with the main air
> flow. This flow will drive down into the cooler air near the floor
> and mix. This warmer air will also want to rise as it is less dense
> than the cooler air in the building and a circulation flow can be
> established. I say can because generally a warehouse is full of racks
> floor to ceiling which will prevent this circulation pattern from
> happening. You are going to have many dead zones which will need
> stratification fans. You may not want all of these fans pushing air
> down. You will need another form of heat independent from the MUA unit
> to provide the rest of the heat the building requires because heating
> a building with 100% OA is not efficient nor would regular building
> require this much fresh air. Consult ASHRAE 62.1 to determine how
> much OA that you need. Consult SB-10 January 2012 of the OBC. You
> will find it will reference ASHRAE 90.1 with exceptions. You must
> follow these codes. They will also dictate your allowable lighting
> loads. If you are dumping a lot of air then heat recovery becomes an
> option. A warehouse can also have a lower heating set point which
> will reduce heat loss through the envelope. They typically don't have
> to be cooled. But that brings up another problem, summer heat. You
> need ventilation to remove heat. Economizers work very well in
> Canada. If you use a AHU with an economizer you don't need a MUA
> unit. A warehouse is a building with tons of mass, over cool it at
> night with an economizer set at 100% exhaust, let the air stratify and
> exhaust the hot air off the bottom of the roof. Go to minimum fresh
> air in the heat of the day and let the mass provide cooling.
> Stratification fans are not bad in the heating season as all the heat
> they make and energy they use stays inside the building.
> This problem comes down to visualization. You can calculate with
> reasonable accuracy if your supply fan discharge will get down to the
> floor. If you do it at an isle crossing you will get 4 circulations
> in the isles. Put a up-blast stratification fan between the supply
> air diffusers to assist. Outboard areas require you to see the air
> flows and decide if an up or a down flow fan gives you the most
> benefit. You can't rip the sheets off the order pickers clip board
> either.
> With your auto size load at 300% you will need to determine why.
> Check your people count, outside air and check infiltration. Compare
> OA to 62.1. Check your envelope losses, compare them to the engineers
> heat loss. When it comes to heat loss OA is the elephant. Check all
> the eQuest defaults, many will have to be changed.
> Bruce Easterbrook P.Eng.
> Abode Engineering
>
> On 09/08/2012 04:57 PM, Adam Barker wrote:
>>
>> Michael,
>>
>> The weather file is representative of the area, and I did run an auto
>> sized load, which calculated heating and airflow capacities much
>> higher than what was specified (about 3x higher on average off the
>> top of my head).
>>
>> You raise a good point regarding de-stratification -- reduced
>> stratification is another claim the company boasts, as the building
>> is pressurized. The claim to cut ACH due to infiltration in half. I
>> believe the team is looking into reducing the # of de-stratification
>> fans in response to this. I searched the forums for how to model
>> de-stratification about 2 weeks ago and came up with a few threads
>> basically hinting that it can't be accurately done. Does anyone have
>> a different opinion, or know if a way where this can at least be
>> approximated? I want to avoid playing with the infiltration rates as
>> I do not believe that is acceptable for a LEED model (at least here
>> in Canada it isn't). As of now I have not modeled this effect.
>>
>> The combustion problem is somehow managed through some limited
>> venting, though I can't remember exactly what is going on, which is
>> why I called them 'direct' fired units.
>>
>> *Adam Barker*, C.E.T., LEED AP BD+C
>>
>> Sustainability Project Manager
>>
>> Provident Energy Management Inc.
>>
>> T: 416-736-0630 x 1874 | abarker at pemi.com <mailto:abarker at pemi.com>
>>
>> *From:*Busman, Michael R [mailto:MBusman at chevron.com]
>> *Sent:* Thursday, August 09, 2012 4:40 PM
>> *To:* Adam Barker; 'equest-users'
>> *Subject:* RE: Cambridge direct fired units in warehouse space
>>
>> Adam,
>>
>> I haven't had any experience with the Cambridge unit, nor am I able
>> to answer your question about the unmet heating hours. Have you
>> tried auto-sizing just for a cfm and Btuh capacity comparison with
>> the mech engineer's load calc? Also, is the weather file
>> representative of the warehouse location?
>>
>> Because the building is a warehouse, it triggered a question in my
>> mind that somebody else might be able to answer. That is if eQUEST
>> models thermal stratification in high bay areas such as warehouses or
>> hangars? If so, it may calculate unmet hours on the coldest days
>> near floor level and a nice warm temperature at ceiling/roof level.
>> Just a wild thought.
>>
>> Mike Busman
>>
>> *Michael R. Busman, CEM*
>>
>> Lead Project Engineer II
>>
>> *Chevron Energy Solutions*
>>
>> A Division of Chevron U.S.A., Inc.
>>
>> 145 S. State College Blvd.
>>
>> Brea, CA 92821
>>
>> Direct 714-671-3561
>>
>> Fax 714-671-3438
>>
>> eFax 866-420-0335 (Include my Full Name followed by "CAI:MHTZ" on
>> Cover Sheet)
>>
>> Mobile 310-387-2083
>>
>> mbusman at chevron.com <mailto:mbusman at chevron.com>
>>
>> *From:*equest-users-bounces at lists.onebuilding.org
>> <mailto:equest-users-bounces at lists.onebuilding.org>
>> [mailto:equest-users-bounces at lists.onebuilding.org]
>> <mailto:[mailto:equest-users-bounces at lists.onebuilding.org]> *On
>> Behalf Of *Adam Barker
>> *Sent:* Thursday, August 09, 2012 1:07 PM
>> *To:* 'equest-users'
>> *Subject:* [Equest-users] Cambridge direct fired units in warehouse space
>>
>> Hello everyone,
>>
>> I was recently asked to model the impact of Cambridge 'direct' fried
>> air handling units for a warehouse building compared to a
>> conventional MUA with supply and exhaust. Has anyone had experience
>> with these units?
>>
>> They boast a very low fan power consumption (5 hp for 8565 cfm of
>> air), 92% thermal efficiency, and a temperature rise and max
>> discharge temp of 160 F.
>>
>> Most of the inputs are straightforward however I am not sure I am
>> modeling the 160 F temperature rise properly. As of now I have
>> Packaged Single Zone systems and have entered 160 F as both the 'zone
>> entering max supply temp' and 'hot deck max leaving temp'. Would this
>> fully capture that temperature rise? I ask as I am getting about
>> 150-200 unmet heating hours in these zones, even though all other
>> inputs are as per the mechanical engineer. Is this significant, or
>> likely just the difference between how eQuest and the mechanical
>> engineer size their loads? The building is a cold climate (southern
>> Ontario, Canada) LEED building, so I want to make sure I am modeling
>> as much benefit as possible.
>>
>> *Adam Barker*, C.E.T., LEED AP BD+C
>>
>> Sustainability Project Manager
>>
>> Provident Energy Management Inc.
>>
>> T: 416-736-0630 x 1874 | abarker at pemi.com <mailto:abarker at pemi.com>
>>
>>
>>
>> _______________________________________________
>> Equest-users mailing list
>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>> To unsubscribe from this mailing list send a blank message toEQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120809/69f3e1e5/attachment-0002.htm>
More information about the Equest-users
mailing list