[Equest-users] LEED modeling garage
Nick Caton
ncaton at smithboucher.com
Fri Aug 17 07:44:50 PDT 2012
I think Karen's second sentence reads better if you tag "... as a direct load to the meter" to the end =).
To the second query, which dances with the "one system per space" rule of DOE2: Something I've done in the past is split a space into two spaces thermally connected with an air wall (copy the space, halve the area/volume/internals, adjust & re-assign the interior partitions for the air wall), then assign the unit heater to one and the cooling system to the other. Carefully review the temperature inputs to ensure the systems aren't fighting each other.
An easier approximation could be to simply include baseboard heating under the system in question.
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Karen Walkerman
Sent: Thursday, August 16, 2012 7:35 PM
To: Michael Campbell
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] LEED modeling garage
if the garage is completely open and unconditioned, then don't model the garage space at all. Simply model the lighting, and any energy used by an exhaust fan for CO and NOx control.
--
Karen
On Thu, Aug 16, 2012 at 2:03 PM, Michael Campbell <mike at sustainablesolutionscorporation.com<mailto:mike at sustainablesolutionscorporation.com>> wrote:
Hello, I just wanted to follow up on this and see if anyone has any information on how to model the garage grilles?
Also one other question - if a space has an AC unit plus and unit heater, how should that be modeled?
Thank you
Mike Campbell, EIT, LEED AP O+M
Sustainability Specialist
(610) 569-1047<tel:%28610%29%20569-1047> office
(610) 569-1040<tel:%28610%29%20569-1040> fax
mike at sustainablesolutionscorporation.com<mailto:mike at sustainablesolutionscorporation.com>
www.SustainableSolutionsCorporation.com<http://www.sustainablesolutionscorporation.com/>
This email message and any attachments are for the sole use of the intended recipient(s) and may contain confidential and privileged information. Any unauthorized review, use, disclosure or distribution is prohibited. If you are not the intended recipient, please contact the sender by reply email and destroy all copies of the original message and any attachments.
From: Michael Campbell [mailto:mike at sustainablesolutionscorporation.com<mailto:mike at sustainablesolutionscorporation.com>]
Sent: Thursday, August 09, 2012 8:47 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: LEED modeling garage
Hello,
I'm currently working on a model for a LEED project. The parking garage is heated only with unit heaters and no cooling. The garage is also ventilated naturally with aluminum grilles. What is the correct way to model this for a LEED project? Also, how do I take the grilles into account? I currently have them in as windows, but I am not sure what do since they are essentially openings in the envelope.
Thank you
Mike Campbell, EIT, LEED AP O+M
Sustainability Specialist
(610) 569-1047<tel:%28610%29%20569-1047> office
(610) 569-1040<tel:%28610%29%20569-1040> fax
mike at sustainablesolutionscorporation.com<mailto:mike at sustainablesolutionscorporation.com>
www.SustainableSolutionsCorporation.com<http://www.sustainablesolutionscorporation.com/>
This email message and any attachments are for the sole use of the intended recipient(s) and may contain confidential and privileged information. Any unauthorized review, use, disclosure or distribution is prohibited. If you are not the intended recipient, please contact the sender by reply email and destroy all copies of the original message and any attachments.
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120817/d9927f06/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120817/d9927f06/attachment-0002.jpg>
More information about the Equest-users
mailing list