[Equest-users] LEED Baseline secondary HVAC system
Ritwik Kakati
rkakati at dagherengineering.com
Fri Aug 17 11:17:01 PDT 2012
Nathan, Maria,
Thanks a lot for your suggestions. I agree with both of you that System
#5 or #7 is quite different from the actual gas-fired constant volume
rooftop unit that will serve the corridors. Maria also made a great
point about Table G3.1.1A having "Building Type" as the header and not
"Space Type".
I think I will go for System #7 since that's where the simplest
interpretation of Exception G31.1.1a leads to, and see what comments I
receive from USGBC about it.
Thanks again to everyone for joining in the discussion.
Ritwik Kakati, LEED Green Associate
Design Engineer
DAGHER ENGINEERING, PLLC
29 Broadway, New York, NY 10006
T. 212.480.2591 x140
F. 212.480.2654
rkakati at dagherengineering.com
www.dagherengineering.com
Save Trees, Consider the Environment. Please print only when necessary.
This email and any attachments may contain confidential or proprietary
information and use or distribution is strictly prohibited. If you are
not the intended recipient, please notify us and delete. Dagher
Engineering, PLLC has no responsibility for errors or discrepancies that
may occur in the electronic transmission of data.
From: Nathan Miller [mailto:nathanm at rushingco.com]
Sent: Friday, August 17, 2012 1:13 PM
To: 'Maria Karpman'; Ritwik Kakati; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] LEED Baseline secondary HVAC system
It kind of falls in that grey-area of whether you get to CHOOSE to apply
the exceptions listed in G3.1.1 or whether you SHOULD apply them if
they are applicable to your project.
The emphasis the in following excerpts is mine.
G3.1.1 exception a states: "Use additional system types for
non-predominant conditions (i.e. residential/nonresidential, or heating
source)...
The same footnote you reference in table G3.1.1A states "Residential
building types include dormitory, hotel, motel, and multifamily.
Residential space types include guest rooms, living quarters, private
living space, and sleeping quarters. Other building and space types are
considered nonresidential.
To me it feels like exception a says use additional system types for
non-resi spaces, such as retail or corridors because they will have
different loads and operational hours, though I can see your point as
well.
I've never had a LEED reviewer tell me to use PTAC/PTHPs for corridors,
but I'd be willing to bet others have used these systems for corridors
and also not received comment on them.
Nathan Miller, PE, LEED AP BD+C
Mechanical Engineer/Senior Energy Analyst
D 206-788-4577 | O 206-285-7100
www.rushingco.com <http://www.rushingco.com/>
From: Maria Karpman [mailto:maria.karpman at karpmanconsulting.net]
Sent: Friday, August 17, 2012 9:07 AM
To: 'Nathan Miller'; 'Ritwik Kakati'; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] LEED Baseline secondary HVAC system
I would argue that residential system type (PTAC/PTHP) should be applied
to the entire multifamily building. The heading of the first column in
Table G3.1.1A is Building Type, not Space Type. The note below the table
reads "Residential building types include dormitory, hotel, motel, and
multifamily....". If the baseline HVAC should be determined solely
based on the conditioned floor area and number of floors of residential
versus non-residential spaces, then why was the building type used as
column heading and in the note below the table? A case study in 90.1
User Manual involves a building with 4 multifamily and 4 non-residential
floors. The 4-storey 54,000 SF non-residential portion in the case study
is modeled with System 5, and the 4 residential floors are modeled with
PTACs. If corridors/stairwells in multifamily buildings are modeled with
non-residential baseline HVAC, then most multifamily buildings over 5
floors would have System 7 serving these areas. I agree with Nathan that
it doesn't makes much sense, especially since most of these spaces are
indirectly conditioned by losses through interior walls of apartments.
Maria
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nathan
Miller
Sent: Friday, August 17, 2012 11:32 AM
To: 'Ritwik Kakati'; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] LEED Baseline secondary HVAC system
Based on the exact wording of the Table G3.1.1A, I would say you are
System 7, which is for "Nonresidential and more than 5 floors OR
>150,000 SF. However, we all can see that it is probably a pretty
ridiculous baseline system for a corridor ventilation unit.
On multifamily projects I've worked on, I've used system 5 in the past
(even though the floor number requirement would trigger system 7) and
never been called on it. That being said, usually that was on projects
with ~7 stories, so I was much closer to the threshold, so maybe the
LEED reviewer just let it slide. Even System 5 is a bit peculiar for a
corridor unit. At least in my climate they end up usually being packaged
rooftop, constant volume units.
Nathan Miller, PE, LEED AP BD+C
Mechanical Engineer/Senior Energy Analyst
D 206-788-4577 | O 206-285-7100
www.rushingco.com <http://www.rushingco.com/>
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Ritwik
Kakati
Sent: Thursday, August 16, 2012 2:09 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] LEED Baseline secondary HVAC system
I am modeling a residential building under LEED 2009. With reference to
ASHRAE 90.1-2007, Exception 'a' in section G3.1.1 which states that we
should use additional system types for nonpredominant conditions if they
apply to more than 20,000 SF of conditioned space - I am confused which
system type I should use for my corridors and other non-residential
conditioned spaces, which are about 21,000 SF total, spread across 20
floors. Do I use System 7, because my non-residential spaces are located
on more than 5 floors, or use System 3 or 5 because the area is less
than 25,000 SF?
Thanks,
Ritwik Kakati, LEED Green Associate
Design Engineer
DAGHER ENGINEERING, PLLC
29 Broadway, New York, NY 10006
T. 212.480.2591 x140
F. 212.480.2654
rkakati at dagherengineering.com
www.dagherengineering.com
Save Trees, Consider the Environment. Please print only when necessary.
This email and any attachments may contain confidential or proprietary
information and use or distribution is strictly prohibited. If you are
not the intended recipient, please notify us and delete. Dagher
Engineering, PLLC has no responsibility for errors or discrepancies that
may occur in the electronic transmission of data.
________________________________
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.2197 / Virus Database: 2437/5204 - Release Date:
08/16/12
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120817/b8743200/attachment-0002.htm>
More information about the Equest-users
mailing list