[Equest-users] Transferring file that has parametric runs to another computer
Dahlstrom, Aaron
ADahlstrom at in-posse.com
Fri Aug 24 13:53:30 PDT 2012
Maria -
I usually copy the PD2, the INP file with the same exact name as the PD2, and the PRD file if it exists. (The additional INP files with " - Baseline Design" or " - X" in the filename are actually generated by eQUEST during a simulation run, and are over-written every time the program runs.) Also, when needed I copy the weather file as Bill mentions.
The remainder I've found can be re-generated by running the model; sometimes I copy-and-paste them anyway if I want to be able to see results without re-calculating. If you're interested, the Modeling Procedures Quick Reference and the Introductory Tutorial have tables showing what each file means and does. (in eQUEST, click "help" -> "tutorials and reference". After opening the PDF, search "PRD")
Re: the invalid argument - I don't actually know all the reasons this pops up. I have had a lot less of these "Invalid Argument" errors once I set my eQUEST up to run "Windows XP (SP2)" compatibility mode, even though I'm on a Windows 7 machine. This can be done by right-clicking the program icon on the desktop, selecting "properties," going to the "compatibility" tab, and modifying the compatibility mode.
All the best,
Aaron Dahlstrom , PE, LEED(r) AP
In Posse - A subsidiary of AKF| 1500 Walnut Street, Suite 1414, Philadelphia, PA 19102
d: 215-282-6753| m: | In Posse: 215-282-6800| AKF: 215-735-7290
e: ADahlstrom at in-posse.com | in posse web: www.in-posse.com<http://www.in-posse.com/> | akf web: www.akfgroup.com<http://www.akfgroup.com/>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bishop, Bill
Sent: Friday, August 24, 2012 9:12 AM
To: Maria Ramos; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Transferring file that has parametric runs to another computer
Maria,
When I want to run a model on a different computer, I open the model and do a "Save-As" to a flash drive, and then open the model from that flash drive on another computer. (I don't copy the files.) I then do a Save-As to a drive on the computer. The only problem I usually have is it can't find a weather file and I have to download it from DOE-2. I'll put the weather file on the flash drive if I remember, since you are out of luck if it is a custom weather file or you don't have an internet connection.
Bill
[cid:image001.jpg at 01CD8218.FC6A18D0]<mailto:wbishop at pathfinder-ea.com>
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org]<mailto:[mailto:equest-users-bounces at lists.onebuilding.org]> On Behalf Of Maria Ramos
Sent: Friday, August 24, 2012 8:50 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Transferring file that has parametric runs to another computer
All, I would like to transfer a simulation with several parametric runs to another computer for a presentation. When I try to run the simulation, it will run all the way to the end, and then say, invalid argument. The baseline run executes just fine, and the parametric runs show up, but won't run. I have tried copying all of the files from the project folder from one folder to the other, and tried copying just the .inps for the 6 parametric runs plus main .pd2 and .inp files, and neither of these worked. Also, the error cites a particular line and character in the .prd file (line 4 character 51) as the problem, but the file which works on my desktop has been copied to the laptop, and it doesn't work. Thanks for any assistance.
Maria
Maria T. Ramos, PE, CxA, LEED B+DC
Innova Engineering, Inc.
2360 Fairview Ave
Cincinnati, OH 45219
T: (513) 419-4235
C: (513) 237-5604
www.innovaengineers.com<http://www.innovaengineers.com/>
mramos at innovaengineers.com<mailto:mramos at innovaengineers.com>
This e-mail may contain information that is confidential, privileged or otherwise protected from disclosure. If you are not an intended recipient of this e-mail, do not duplicate or redistribute it by any means. Please delete it and any attachments and notify the sender that you have received it in error. Unintended recipients are prohibited from taking action on the basis of information in this e-mail. E-mail messages may contain computer viruses or other defects, may not be accurately replicated on other systems, or may be intercepted, deleted or interfered without the knowledge of the sender or the intended recipient. If you are not comfortable with the risks associated with e-mail messages, you may decide not to use e-mail to communicate with In Posse.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120824/d2598aaa/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 20869 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120824/d2598aaa/attachment-0002.jpg>
More information about the Equest-users
mailing list