[Equest-users] u-values
Umesh Atre
umesh at innovativedesign.net
Thu Aug 30 09:59:17 PDT 2012
Tim,
Looks like you just happened to choose an inefficient door from the
library. You selected an uninsulated sgl lyr in your model.
Depending on your choice, the u-values will change. In the model below,
I have selected 3 different doors, for example.
With that said, and as the reviewer commented, I would advise not using
any defaults unless you do not happen to know the door constructions in
your design.
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of tim
Sent: Thursday, August 30, 2012 11:41 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] u-values
I let my eQuest model generate U-values (see LV-I report - page 2 of
attached pdf)
The U-values don't seem to make any sense. The LV-I report says a door
has a U-value of 2.080.
I looked up hollow metal insulated doors on the internet and found one
that has a value of 0.16.
Why is there such a difference?
I know how to change u-values in detailed edit mode, but wonder what
experience others have had with determining what U-values should be
used.
I used an online calculator to find the u-value for a wall like mine
(also attached).
Having trouble figuring out how to determine/ enter u-value for a roof
assembly that is a trussed attic with insulation above ceiling as well
as others.
I also realize ASHRAE has basic u-values listed, but my leed reviewer
commented saying ASHRAE U-values should be used only if the actual
U-values are unknown. I assume this means if the makeup of a wall or
assembly cannot be determined.
Thanks for your help in advance!
Timothy W. Hill
tim.JRGA at fuse.net
John R. Grier, Architect
11309 Deerfield Road
Cincinnati, Ohio 45242
(513)489-3690
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120830/5aa63cbf/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 12034 bytes
Desc: attdb2a5.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120830/5aa63cbf/attachment-0002.jpeg>
More information about the Equest-users
mailing list