[Equest-users] Warehouse configuration on Ashrae
Robby Oylear
robbyoylear at gmail.com
Thu Aug 30 13:26:46 PDT 2012
Interesting. When this first popped up I thought it only applied to
warehouses, but with the addition of exception (e) to G3.1.1 it would
appear this can be used for stairwells, vestibules, mechanical rooms.
Thanks for the info.
Robby Oylear, PE, LEED AP
Mechanical Engineer
Senior Energy Analyst
D 206-788-4571
www.rushingco.com
On Thu, Aug 30, 2012 at 1:13 PM, Stormy L. Shanks <shankssl at kjww.com> wrote:
> Hi, Karen – You can follow addendum dn to ASHRAE 90.1 2007. You can find
> a PDF of it by googling “addendum dn”. It addresses this situation with the
> addition of HVAC baseline system types 10 and 11, which are for “heated
> only storage.” I’m still working on fully understanding the addendum myself
> for a similar building – a hangar with attached office/support. Prior to
> this addendum, you would have had to model the warehouse with cooling even
> though there isn’t any. The typical loophole was to set thermostat
> schedules with really high setpoints in cooling mode in the hopes of the
> cooling never turning on, which sort of worked, but the addendum should
> make it much more realistic. ****
>
> ** **
>
> Good luck!****
>
> ** **
>
> *Stormy Shanks, PE*****
>
> Mechanical Engineer ****
>
> www.kjww.com****
>
> ** **
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Karen Smith
> *Sent:* Thursday, August 30, 2012 2:51 PM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Warehouse configuration on Ashrae****
>
> ** **
>
> Hi all,****
>
> ** **
>
> Im a bit confused with the classification of Ashrae 90.1 2007, Im
> currently modeling a facility of a total of 47,600 SF including a 28,000 SF
> Warehouse. The facility includes 2 levels of offices, breakrooms, etc and a
> double height warehouse adjacent to them. The proposed design is composed
> of 2 AHUs, one for the first floor, one for the second and a only heating
> and ventilation system based on 2 boilers for the warehouse. According to
> this, the baseline should be a System 5 Packaged VAV with Reheat, Packaged
> rooftop VAV with reheat, Direct expansion cooling type and Hot-water
> fossil fuel boiler for heating. One system per floor, but my confusion is
> on the part of the warehouse. Should I model an additional Cool and Heat
> System for the warehouse even though in the proposed we have it as only
> heating and ventilation system? If so, does it have to be the same type of
> system specified (System 5) or can it be System 3 or 4 instead?****
>
> ****
>
> Thanks.****
>
> ** **
>
> Karen Smith****
>
> Sustainable Solutions, Inc****
>
> (404) 784.7061****
>
>
> ------------------------------
> *This message and any attachments contain information intended for a
> specific party and may include sensitive or confidential material. If you
> are not the intended recipient, please do not read, copy, use, or disclose
> to others. Please notify the sender of the delivery error by reply and then
> permanently delete this message and all attachments.*
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120830/5198dadf/attachment-0002.htm>
More information about the Equest-users
mailing list