[Equest-users] Baseline CFM

Gastón Michaud F. gaston.michaud at cts-cr.com
Thu Dec 6 10:11:21 PST 2012


Good morning everyone,

We are having an issue with the calculated total fan flow of the baseline case and was wondering if someone could help me out.  We are modeling a 12 floor hotel, with a VRF system in the first three floors and PTAC's in the remaining 9 (rooms); for a total conditioned area of about 92325 sf.  The baseline case is modeled with a system 2 per ASHRAE appendix G.
The following table summarizes our issue:


Baseline case

Proposed case

Total cooling capacity

281.5 tons

247 tons

Design airflow rate

39700 cfm

80500 cfm


We used the automatic calculation from eQuest (leaving both capacity and fan flow blank) for the baseline case, and the actual mechanical design for the proposed case.  For some reason, the baseline calculation for the fan flow seems to be very low, and was wondering if anyone has had a similar issue regarding the automatic calculations from eQuest.  If so, has anyone found a solution?

If we analyze other estimates, eQuest is calculating about 0.43 cfm/sf for the baseline, which also seems very low compared to other projects we have worked with.  We are also thinking of using the following formula to estimate the baseline fan flow: Sensible btu=1.09*cfm*dT; but with this approach we get a fan flow about 50% more that the proposed, which also seems unlikely.  Any suggestions for estimating the baseline fan flow which LEED reviewers accept?

Thanks you very much, hope someone can help us out.

  Ing. Gastón Michaud F.
  Tel.: (506) 2222-7529
  Fax: (506) 2256-5608
  From USA: 1-305-433-3668
  Calle 30, Avenida 0 y 2. San José, Costa Rica

[Description: Description: Description: Description: Description: LEEDAP_BDCbw]

[Description: Description: Logo CTS firma]
Este correo puede contener información protegida por el secreto profesional. Si usted no es la persona a quien va dirigido, por favor tome en cuenta que su divulgación, distribución o reproducción es estrictamente prohibida. Cualquier persona que reciba este mensaje por error debe notificarlo inmediatamente al remitente vía telefónica o correo electrónico y borrarlo permanentemente de su computador. Los comentarios plasmados en este correo son del remitente solamente y no reflejan necesariamente la posición de CTS S.A.
Por favor considere su responsabilidad con el medio ambiente antes de imprimir este correo electrónico
----------------------------------------------------------------------------------------------------------------
This mail may contain information that is legally privileged, confidential or exempt from disclosure.  If you are not the intended recipient, please note that any dissemination, distribution or copying of this message is strictly prohibited.  Anyone who receives this message in error should notify the sender immediately by telephone or by e-mail and delete it permanently from their computer.  The opinions above are those of the author and do not necessarily reflect the position of CTS S.A.
Please consider your environmental responsibility before printing this e-mail

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20121206/cbad027f/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 2289 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20121206/cbad027f/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 5468 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20121206/cbad027f/attachment-0001.jpg>


More information about the Equest-users mailing list