[Equest-users] Baseline CFM
David Griffin
dgriffin at etcgrp.com
Thu Dec 6 13:12:40 PST 2012
Gaston,
I agree with Mike. When I have run into the issue in the past, I have solved it by reviewing my schedules and internal loads to make sure they are realistic.
Thanks,
David Griffin
Energy Analyst
ETC Group, LLC
801.278.1927 ext. 128
Cell 480.235.0899
Fax 801.486.0668
dgriffin at etcgrp.com<mailto:dgriffin at etcgrp.com>
[Copy of ETC_LogoOnly2_rgb_sm.png]
1997 South 1100 East, Suite 201, Salt Lake City, UT 84106-4471 - www.etcgrp.com<http://www.etcgrp.com/>
-------------------------------------------------------------------------------------------------------------------
CONFIDENTIALITY NOTICE This e-mail transmission, and any documents, files or previous e-mail messages attached to it may contain confidential information that is legally privileged. If you are not the intended recipient or the person responsible for delivering it to the intended recipient, you are hereby notified that any disclosure, copying, distribution or use of any of the information contained in or attached to this transmission is strictly prohibited. If you have received this transmission in error, please immediately notify us by telephone at (801) 278-1927 and destroy the original transmission and its attachments without reading them. Thank you.
From: Busman, Michael R [mailto:MBusman at chevron.com]
Sent: Thursday, December 06, 2012 12:34 PM
To: Gastón Michaud F.; equest-users at lists.onebuilding.org
Cc: Eric Fischel J.
Subject: Re: [Equest-users] Baseline CFM
Gaston,
I don't know if this will help you or not. I don't claim to be an expert in eQUEST, however, I started doing hourly simulations about 1983 and in another life, spent 17 years with Hilton Hotels Corp., so I do know a little about how hotels operate.
I have found that simulations aren't the greatest for sizing systems versus a load design program, except maybe in the case of a central plant where load diversity can be accounted for. In a hotel, you need to design for worst case or almost worse case conditions in the individual spaces even though they may not operate that way. A couple of examples. For the guest room PTAC units, you probably need to size for the draperies open, guests in the room, and maybe the TV or a couple of lights on. In reality, the guest is out of the room most of the day and the maid probably closes the draperies and turns off the TV and lights. So, you might simulate how the room is occupied and used versus sizing the PTAC capacity. As another example, if the guest is out of the room, he/she is probably out of the hotel, in the restaurant, or perhaps, in a meeting in the ballroom. Since the guest cannot be in two places at once, you need to look at the sizing versus the operation of the public spaces. Generally a ballroom area will have a large prefunction/registration/coffee break area outside the ballroom. If you decide you want 2 systems, one for the ballroom and one for the prefunction area, you'll size the systems for the peak load of those spaces. If you decide to design a single VAV system for both the ballroom and prefunction area, you will have a smaller system than the total capacity of the two separate systems as it will track the load as guests move back and forth between the ballroom and prefunction area.
It sounds like the VRF systems for the first 3 floors were designed/sized on the airside for the peak load of the separate spaces, but the cooling capacity took diversity into account, similar to a central chiller plant.
You might want to look at how you defined the separate spaces and the amount of internal load diversity from the hourly schedules.
I hope John Aulbach will chime in. He's been using DOE-2 since you had to chisel the calcs on a stone tablet and was a consultant to Hilton for many years, so he also knows how hotels operate.
My best,
Mike Busman
Michael R. Busman, CEM
Lead Project Engineer II
Chevron Energy Solutions
A Division of Chevron U.S.A., Inc.
145 S. State College Blvd.
Brea, CA 92821
Direct 714-671-3561
Fax 714-671-3438
eFax 866-420-0335 (Include my Full Name followed by "CAI:MHTZ" on Cover Sheet)
Mobile 310-387-2083
mbusman at chevron.com<mailto:mbusman at chevron.com>
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Gastón Michaud F.
Sent: Thursday, December 06, 2012 10:11 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Cc: Eric Fischel J.
Subject: [Equest-users] Baseline CFM
Good morning everyone,
We are having an issue with the calculated total fan flow of the baseline case and was wondering if someone could help me out. We are modeling a 12 floor hotel, with a VRF system in the first three floors and PTAC's in the remaining 9 (rooms); for a total conditioned area of about 92325 sf. The baseline case is modeled with a system 2 per ASHRAE appendix G.
The following table summarizes our issue:
Baseline case
Proposed case
Total cooling capacity
281.5 tons
247 tons
Design airflow rate
39700 cfm
80500 cfm
We used the automatic calculation from eQuest (leaving both capacity and fan flow blank) for the baseline case, and the actual mechanical design for the proposed case. For some reason, the baseline calculation for the fan flow seems to be very low, and was wondering if anyone has had a similar issue regarding the automatic calculations from eQuest. If so, has anyone found a solution?
If we analyze other estimates, eQuest is calculating about 0.43 cfm/sf for the baseline, which also seems very low compared to other projects we have worked with. We are also thinking of using the following formula to estimate the baseline fan flow: Sensible btu=1.09*cfm*dT; but with this approach we get a fan flow about 50% more that the proposed, which also seems unlikely. Any suggestions for estimating the baseline fan flow which LEED reviewers accept?
Thanks you very much, hope someone can help us out.
Ing. Gastón Michaud F.
Tel.: (506) 2222-7529
Fax: (506) 2256-5608
From USA: 1-305-433-3668
Calle 30, Avenida 0 y 2. San José, Costa Rica
[Description: Description: Description: Description: Description: LEEDAP_BDCbw]
[Description: Description: Logo CTS firma]
Este correo puede contener información protegida por el secreto profesional. Si usted no es la persona a quien va dirigido, por favor tome en cuenta que su divulgación, distribución o reproducción es estrictamente prohibida. Cualquier persona que reciba este mensaje por error debe notificarlo inmediatamente al remitente vía telefónica o correo electrónico y borrarlo permanentemente de su computador. Los comentarios plasmados en este correo son del remitente solamente y no reflejan necesariamente la posición de CTS S.A.
Por favor considere su responsabilidad con el medio ambiente antes de imprimir este correo electrónico
----------------------------------------------------------------------------------------------------------------
This mail may contain information that is legally privileged, confidential or exempt from disclosure. If you are not the intended recipient, please note that any dissemination, distribution or copying of this message is strictly prohibited. Anyone who receives this message in error should notify the sender immediately by telephone or by e-mail and delete it permanently from their computer. The opinions above are those of the author and do not necessarily reflect the position of CTS S.A.
Please consider your environmental responsibility before printing this e-mail
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20121206/fa1b0bf7/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1559 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20121206/fa1b0bf7/attachment-0006.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 2289 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20121206/fa1b0bf7/attachment-0007.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 5468 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20121206/fa1b0bf7/attachment-0008.jpg>
More information about the Equest-users
mailing list