[Equest-users] Cooling EIR
Daniel Kaler
DanielK at mepassociates.com
Tue Feb 7 10:39:15 PST 2012
Hi All,
I don't mean to ask questions back to back days here, but I ran into roadblock. I found an equation for the compressor EIR to be:
Cooing EIR=(1/EER-0.012167)/(1/3.413-0.012167)
Has anyone tried to derive this, or know of a document that has done so? I seem to be missing something in my derivation as follows:
* EER=Cooling Output (Btuh)/(Supply Fan Input (W) + Compressor Input (W))
* 1/EER=Supply Fan Input/Cooling Output + Compressor Input/Cooling Output
* Compressor Input/Cooling Output = 1/EER - Supply Fan Input/Cooling Output
At ARI condition supply fan is rated at 365W/CFM & 400CFM/Ton
So Supply Fan Input/Cooling Output = 0.146 kW/Ton or .012167 W/Btuh
* Compressor Input/Cooling Output = 1/EER - 0.012167
* Compressor Input/Cooling Output (Btu/Btu) = 3.413*(1/EER - 0.012167)
i.e.
EER=11
Compressor EIR = 3.413*(1/11 - 0.012167) = 0.2687 (should be 0.2580)
Is there something that I am missing?
Thank in advance,
Daniel Kaler
Energy Engineer, EIT
MEP ASSOCIATES
engineers | consultants | commissioning
MEP Associates, LLC | 2720 Arbor Court | Eau Claire, WI 54701
Phone: 715.832.5680 | Fax: 715.832.5668 |www.mepassociates.com