[Equest-users] Dummy Zone & DOAS with heat wheel recovery
Brian Fountain
bfountain at greensim.com
Fri Feb 3 07:19:25 PST 2012
Note that at this point, the OA-FROM keyword is just setting the OA
temperature for the borrowing system to the return air temperature for
the lending system. It isn't really modelling DOAS yet. The issue this
leads to is the heat recovery device is seeing the exhaust air stream
temperature from the dummy zone, not the borrowing zones.
In heating dominated climates, this can be overcome by either adding a
dummy internal load to the dummy zone to give it a higher return air
temp for heat recovery or what I do is use the frost control to force
the exhaust air stream temperature up to a reasonable value (73F) and
put that as electric heat on a separate, free meter. In a cooling
dominated climate, I don't know how you would force that dummy zone
return temperature down.
On 2/3/2012 7:44 AM, Soham Babu wrote:
>
> ·Create Dummy space & dummy zone
>
> ·Create DOAS as system as package single zone assign to dummy Zone
>
> · For other system outside air from DOAS.
>
> *From:*equest-users-bounces at lists.onebuilding.org
> [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of
> *RIAD ABED
> *Sent:* Friday, February 03, 2012 2:46 PM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Dummy Zone & DOAS with heat wheel recovery
>
> */Dear All e-Quest Users/*
>
> */
> /*Please how to model a *Dummy Zone*& *DOAS with heat wheel
> device*(dedicated outdoor outside air) in e-Quest....I need it please
> very urgent ...if somebody please help me.....Your reply is very very
> highly appreciated ...thanks by Advance
>
> My Regards,
> *Riad el Abed*
> *Chief MEP , PQP*
> Tel +96170 643977
>
> *DEC Consultants*
> Po Box 26330
> Abu Dhabi
> Tel +9712 4457505
> Fax +9712 4457506
> www.dec.ae
>
> _____________________________________________________________________
>
> *DISCLAIMER*
>
> This email and any files transmitted with it are confidential and
> intended solely for the use of the individual or entity to whom they
> are addressed. If you have received this email in error please notify
> the sender. Please note that any views or opinions presented in this
> email are solely those of the author and do not necessarily represent
> those of DEC Consultants. Finally, although efforts were made to
> prevent virus transmission, the recipient should check this email and
> any attachments for the presence of viruses. DEC Consultants accepts
> no liability for any damage caused by any virus transmitted by this email.
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120203/93c080b3/attachment-0002.htm>
More information about the Equest-users
mailing list