[Equest-users] Exhaust fan based on temp
Chris Jones
cj at enersave.ca
Wed Feb 8 09:11:12 PST 2012
You can turn the exhaust fan around - create a packaged single zone
system with a very small cooling capacity, schedule it off for
heating and set the cooling setpoint the same as the setpoint for the
exhaust fan to turn on. It take a bit of optimizing so you don't end
up increasing the heating load.
At 11:22 AM 08/02/2012, R B wrote:
>Looks like I can do this is if make the space as sunspace. Anything
>else to worry about if it is a sunspace - never used this before. I
>am assuming that the vented air is made up by the AHU system in the space.
>Thanks
>-Rohini
>
>On Wed, Feb 8, 2012 at 10:10 AM, R B
><<mailto:slv3sat at gmail.com>slv3sat at gmail.com> wrote:
>Is there a way to model exhaust fans based on temperature or any
>workaround? I thought this would be straightforward to do but am
>going blank on this - this is for large spaces like atrium, or
>generator rooms, attic spaces etc.
>
>Thanks
>-Rohini
>
>
>_______________________________________________
>Equest-users mailing list
>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>To unsubscribe from this mailing list send a blank message to
>EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
Chris Jones
14 Oneida Avenue
Toronto, ON M5J 2E3.
Tel. 416-203-7465
Fax. 416-946-1005
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120208/d49985bb/attachment-0002.htm>
More information about the Equest-users
mailing list