[Equest-users] Changing Weather Data for Detailed Model w/Parametric Runs
Patrick J. O'Leary, Jr.
poleary1969 at gmail.com
Thu Feb 16 12:38:37 PST 2012
open the .pd2 file with notepad or something else. the weather file
location is right at the top. just type in the name you want after the
tmy\ , but don't forget the closing quote.
Proj "Project name"
ProgramVersion = "eQUEST 3.63.6510"
BDBaseVersion = 24
ProductCode = "eQUEST"
WeatherFile = "TMY2\TUCSONAZ.bin"
On 2/16/12 1:11 PM, Sandy LaFlamme wrote:
>
> Hi,
>
> I'm trying to modify detailed eQUEST 3.64 models with parametric runs
> that were created by someone else. I need to change the weather
> locations.
>
> I thought I should be able to change it on the Site Data form on the
> Component Tree. However, the Site Data form is missing the weather
> file location input option.
>
> Does anyone know if this is a bug in the model or a problem with
> eQUEST? Is there another way I can change the weather location and
> have it change for both the baseline and parametric runs? I did try
> double-clicking on the "Project" form at the top of the Component Tree
> and it does let me change the weather file there, but it is only
> changing it for the baseline run and not the parametric run. Thank
> you for the help!
>
> Sandy
>
> P.S. Here is the Site Data form I'm seeing, without the weather
> location input option:
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120216/89952679/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 13916 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120216/89952679/attachment-0002.png>
More information about the Equest-users
mailing list