[Equest-users] Heat Recovery Chiller
Michael Wilson
mwilson at enerficiency.ca
Thu Feb 16 21:58:25 PST 2012
Hi Michael. HTREC-DT has to be less than 70. Thats found on the Loop
Attachments tab of your chiller. It defaults to the dT of your HW loop, so
if thats over 70 you'll need to change the value of HTREC-DT.
Mike
Michael Wilson, P.Eng., Enerficiency Consulting
PO Box 1911 - 458 Abbs Rd., Gibsons, BC V0N 1V0 | 604-886-9864 |
www.enerficiency.ca
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Michael
Hupel
Sent: February-16-12 2:37 PM
To: 'Equest Users'
Subject: [Equest-users] Heat Recovery Chiller
I am modeling a building that will have one chiller as a heat recovery
chiller. The design will heat reject into the domestic water loop. I am
seeing a BDL error saying HTREC-DT must be less than or equal to 70.
Without clearing this error I am not able to run a simulation. Can anyone
advise how to clear this error?
As always I am grateful to this community of experts.
Thanks
Mike Hupel, B.Tech, CEM, LEED AP
Senior Mechanical Designer
56 Pennsylvania Ave.
Concord, ON, L4K 3V9
(905) 761-1264 ext. 24
(905) 761-6949 fax
_____
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.1913 / Virus Database: 2112/4813 - Release Date: 02/16/12
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120216/050a248b/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 2819 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120216/050a248b/attachment-0002.gif>
More information about the Equest-users
mailing list