[Equest-users] Humdity control
Brian Fountain
bfountain at greensim.com
Wed Feb 22 05:45:53 PST 2012
Set max humidity keyword to 55%. Supply air temperature will be reset
down for humidity control down to minimum supply air temperature if
required. Set reheat delta T and heating source -- and watch for
underheated hours if there is insufficient reheat.
On 2/22/2012 7:27 AM, sambhav tiwari wrote:
> Hi All,
> I have a VAV system where duct heaters are installed to
> control space humidity if exceeds 55% how can i model it .
>
> Thanks
> Sambhav Tiwari
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
More information about the Equest-users
mailing list