[Equest-users] Translucent Glass Overhangs?
Neil Bulger
nbulger at integralgroup.com
Tue Jan 17 10:32:23 PST 2012
Hi everyone,
I have a building with frosted glass overhangs that are fairly large, about 10 feet out. I am only concerned with the energy component of my model and do not have any daylighting controls so this should make things easier. My gut tells me the frosted overhang will reduce and potentially eliminate the direct solar heat gain component. Has anyone studied this?
Thanks,
Neil Bulger
________________________________
I N T E G R A L
GROUP
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Sami, Vikram
Sent: Tuesday, January 17, 2012 7:20 AM
To: Pranita Kothuru Komirishetty; equest-users
Subject: Re: [Equest-users] Calculate energy usage of individual buildings in a campus
Pranita,
Could you create a secondary loop for each chiller? You could then get the numbers you need from the PS-D or PS-H report.
Vikram Sami, LEED AP BD+C
Sustainable Design Analyst
1315 Peachtree St. NE, Atlanta, GA 30309
t: 404-443-7462 f: 404.892.5823 e: vikram.sami at perkinswill.com www.perkinswill.com<http://www.perkinswill.com/>
Perkins+Will. Ideas + buildings that honor the broader goals of society
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Pranita Kothuru Komirishetty
Sent: Monday, January 16, 2012 6:08 PM
To: equest-users
Subject: [Equest-users] Calculate energy usage of individual buildings in a campus
Hello All -
I am modelling a campus in eQuest which has 7 building. All building are connected to the central chiller and boiler. I am trying to figure out how much of the chiller capacity each building is using from the chiller and how much of the boiler capacity each building is using.
Which reports in eQuest give this breakdown of eneryg usage? OR Do we have to calculate these number, if so please give a brief explanation.
Thank You.
--
- Pranita
This email and any files transmitted with it are confidential and intended solely for the addressee. If you are not the named addressee you should not disseminate, distribute, copy, or alter this email.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120117/070e4efa/attachment-0002.htm>
More information about the Equest-users
mailing list