[Equest-users] Heating Only Zones
Hall, Brendan
BHall at karpinskieng.com
Wed Jan 25 06:44:45 PST 2012
Hey all,
I need help with a comment that I got back on my final review. I have a 4 zones that are heating only, two are storage rooms with only unit heaters and two are vestibules with air curtains. I was told I need to put cooling into those spaces identical to the baseline per Table G3.1 Proposed 10d. Makes sense. I am using a system 6 so I switched my system type to package single zone so I could have DX cooling to match the baseline and electric heating to match my proposed in the same zone. My question is in what air volume and fan energy I should use. Should I use the CFM and fan kW that was scheduled or let it auto size at 20° dT and use the ASHRAE fan energy equation? It seems that either way I go I am either going against putting in the proposed building as scheduled or having identical cooling in both.
I am in the position of having to appeal so I need to get this to a satisfactory point on the first try. Any suggestions are welcome and appreciated.
Brendan Hall, M.Sc., LEED AP BD+C
Engineer, Mechanical
karpinski
ENGINEERING
3135 Euclid Avenue
Cleveland, OH 44115
P 216.391.3700 x 3111
E bhall at karpinskieng.com<mailto:bhall at karpinskieng.com>
W www.karpinskieng.com<http://www.karpinskieng.com/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120125/f007f378/attachment-0002.htm>
More information about the Equest-users
mailing list