[Equest-users] Internal Wall Problems with Wizard
Robby Oylear
robbyoylear at gmail.com
Tue Jul 10 08:52:45 PDT 2012
Omer,
The simplest way to ensure that eQUEST defines the NEXT-TO property
correctly is to make sure that each interior wall only interfaces with one
other interior wall.
In the situation you describe where you have an interior wall that is
adjacent to more than one zone, I would typically split that interior wall
into two or three walls by adding vertices at each of the intersections
between the zones and the interior wall that spans them.
Here's a sketch of what I'm describing:
[image: Inline image 1]
Hope that helps.
Robby Oylear, PE, LEED AP
*Mechanical Engineer*
*Senior Energy Analyst*
* *
*D* 206-788-4571
*www.rushingco.com* <http://www.rushingco.com/>
On Tue, Jul 10, 2012 at 8:45 AM, Ömer Moltay <omoltay at mimtarch.com> wrote:
> Dear All,
>
> I have realized that while creating the model after Wizard entries, eQuest
> will fail to determine the NEXT-TO property for interior walls that are
> adjacent to more than one zone and all those interior walls will be defined
> as ADIABATIC.
>
> Also, I see that interior walls are missing from zones where another zone
> has an ADIABATIC wall in the same place.
>
> I see no way of having a model with all interior walls correctly defined
> without fixing all these problems after the Wizard. Does everybody have the
> same experience or am I missing something?
>
> Ömer Moltay, LEED AP BD+C, ASHRAE BEMP, CPMP, BREEAM Assessor
> Mimta EcoYapi
> Hekimsuyu Cad. 559. Sk. No:39
> 34255 Kucukkoy Istanbul Turkey
> Tel: 90-212-617-2296
> Fax: 90-212-617-2297
> www.ekoyapi.net
> www.mimtasolar.com
> www.mimtarch.com
>
>
> ______________________________**_________________
> Equest-users mailing list
> http://lists.onebuilding.org/**listinfo.cgi/equest-users-**onebuilding.org<http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org>
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE@**ONEBUILDING.ORG<EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
> ______________________________**_________________
> Equest-users mailing list
> http://lists.onebuilding.org/**listinfo.cgi/equest-users-**onebuilding.org<http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org>
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE@**ONEBUILDING.ORG<EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120710/7485cab7/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 10321 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120710/7485cab7/attachment-0002.png>
More information about the Equest-users
mailing list