[Equest-users] WSHP(Heating HW loop has zero design flow) vs PVVT, PSZ, etc
Brian Fountain
bfountain at greensim.com
Mon Jul 16 13:07:11 PDT 2012
Change your condenser loop type from condenser to water source heat pump.
That will allow you to put both your boilers and your cooling tower on the
same loop. Then delete the hot water loop as it is not used in the model.
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nikola
Kravik
Sent: Monday, July 16, 2012 3:23 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] WSHP(Heating HW loop has zero design flow) vs PVVT,
PSZ, etc
Hi,
I'm trying to model WSHP's served by Closed circuit Fluid Cooler and Boiler.
I get the below error if I use WSHP; I
I read the users archive from Bill Bishop, Umesh and others about WSHP
approximations to PVVT or PSZ but when trying to run simulation it still
kicks me out saying "zero design on the hhw loop" anything I'm missing?
Thanks,
Nikola
Nikola Kravik, LEED AP Description: cid:image001.gif at 01CB9AE0.30118F00
Project Engineer
Willdan Energy Solutions
6130 Stoneridge Mall Road, Suite 380
Pleasanton, CA 94588
T. 925.416.4200 ext. 1228
D. 925.416.4228
C. 925.719.5883
F. 925.737.0174
<mailto:nkravik at willdan.com> nkravik at willdan.com
<http://www.willdan.com/energy> www.willdan.com/energy
WD_tagend_300rgb
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120716/e0d5764d/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 261368 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120716/e0d5764d/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 1348 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120716/e0d5764d/attachment-0002.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 3030 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120716/e0d5764d/attachment-0002.jpeg>
More information about the Equest-users
mailing list