[Equest-users] Unmet heating hours and space loads don't match up
Walson, Kristy
kristy.walson at tlc-eng.com
Thu Jun 7 13:53:20 PDT 2012
Hi all,
I need some help figuring out the source of unmet heating hours right now. Using RTU 4-2 as the example (only 2 zones), here is the load summary for these spaces (spaces are highlighted in black):
[cid:image002.png at 01CD44CE.0B3EA8E0][cid:image005.jpg at 01CD44CC.99A7CAA0]
The best I can tell from this report (correct me if I'm wrong) is that the spaces require approximately 38.5 kBtu/h total of heating to satisfy the load. The unit has 430 kBtu/h (or rather, MBH) of heat. Yet, I still have a ton of unmet heating hours. The unit is constant volume. Thoughts?
Kristy M. Walson, PE, LEED AP BD+C, BEMP
Associate / Sustainability Consultant
TLC Engineering for Architecture
Your 2030 Challenge Partner
255 South Orange Avenue, Suite 1600
Orlando, FL 32801-3463
phone:
407-841-9050
fax:
407-425-7367
direct:
407-487-1118
website:
www.tlc-engineers.com<http://www.tlc-engineers.com>
[cid:image004.gif at 01CD44CC.98DB04C0]<http://www.tlc-engineers.com/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120607/2bcc4d09/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.gif
Type: image/gif
Size: 5272 bytes
Desc: image004.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120607/2bcc4d09/attachment.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 142164 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120607/2bcc4d09/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 835 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120607/2bcc4d09/attachment.png>
More information about the Equest-users
mailing list