[Equest-users] air flow sizing
sambhav tiwari
tiwari.sambhav at gmail.com
Mon Jun 11 22:38:07 PDT 2012
Hi All,
The cfm for zone is sized based on room and supply air
temperature deltaT and room sensible heat load ie
cfm=RSHL(btu/hr)/(1.08XdeltaTinF)
similarly the cfm for the latent load is
cfm=RLHL(btu/hr)/(4840XdeltaW) Where deltaW is Ws-Wr ,Ws is humidity
ratio lb of water/lb of dry air of supply air at 55F and Wr is room
design humidity and RLHL is latent load in btu/hr
the total cfm should be sum of both due to deltaT and deltaW
But equest takes only due too sensible load because there is no where
option to input supply air humidity and room design humidity
then how it takes in account of cfm due to deltaW?
Thanks
Sambhav
More information about the Equest-users
mailing list