Oh - funny my response is coming in right behind Brian!

In the wizards you can assign exhaust quantities for specific zones at the zone group definitions screen (towards the end while editing a shell).

Assigning a quantity here during wizards is good for a placeholder in my experience, but I generally plan for giving all exhaust inputs and associated scheduling a second pass during detailed mode for review and further editing, to be sure I'm capturing the correct behavior.

An extra caution comes to mind:  zonal exhaust bypasses any attempts at heat recovery, so one should come up with a strategy during the wizards if you're dealing with central unit energy recovery and/or recovering DOAS's.

If anyone needs a refresher in energy recovery, I advise searching for 'Brian Fountain recovery' in the archives.  For the current version of eQuest (3.64), I think this guy and fellow list contributors have nailed most sides of the topic down pretty well in layman's terms.  There's also a thread from some years back I've personally referenced often where Brian helped me get a grip on how system level exhaust is more-or-less indirectly defined...

~Nick

[cid:489575314 at 22072009-0ABB]

NICK CATON, P.E.
SENIOR ENGINEER

Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Brian Fountain
Sent: Wednesday, June 06, 2012 9:26 AM
To: 'Pasgar, Arash'; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] EF

You can include zonal exhaust in the zone groups screen (14) of the DD wizard.  I tend to define zonal exhaust (along with other HVAC details) in the detailed interface.

From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Pasgar, Arash
Sent: Wednesday, June 06, 2012 10:11 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] EF

Hi All,

I have a RTVAV system with 10 VAVs that serve the building. Some of the space have exhaust fan (such as hydraulic assembly).
I am on DD wizard. Should I model them at this level or later? And how?

Thank you,

Arash Pasgar
Mechanical Designer

[Description: Description: Description: Description: Description: Description: image001]

v. 210.546.0200 | www.dbrinc.com<http://www.dbrinc.com>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120606/e379f234/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120606/e379f234/attachment-0004.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 4870 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120606/e379f234/attachment-0005.jpg>


More information about the Equest-users mailing list