I wanted to build upon the other reply - DCV in this case probably takes another form, such as reducing minimum airflow when labs are unoccupied or reduced fume hood exhaust when no users are present.
These you'll have to arrange by making customized schedules rather than using the CO2-based DCV module built in to eQUEST.
Your HVAC consultant will have to explain the proposed sequence of operation for the AHUs in a little more detail. CO2 is often used as a surrogate for other contaminants related to the building occupants.
In your case for a laboratory building the contaminants from the occupants may not be a chief concern, so it doesn't seem likely that eQUEST's built-in DCV is what you should be using.
Could the system operate more along the lines of this perhaps: http://www.i2sl.org/elibrary/documents/sharp.pdf
David
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of sambhav tiwari
Sent: Saturday, June 09, 2012 5:15 AM
To: equest-users
Subject: [Equest-users] DCV
Hi All,
How can i model DCV for a laboratory building with 100%
fresh air ie no recirculation.
Since there is no return air path here so HVAC consultant says that
CO2 sensors will be placed in the occupied zones between 3 to 6ft, and
fresh air ie supply air will be modulated based on CO2 ppm
differential of outside and zone air.
But if when i tried to do it by making OA control method as DCV zone
sensors in OA and economizer tab in Air size system HVAC i am getting
75% reduction in my cooling energy which is unimaginable.
I look forward for any response.
Thanks
Sambhav.