John, you are correct. REHEAT-DELTA-T is set at the system level and
applies to all zones on that system. The ability to meet the heating
load will depend on the minimum flow during heating mode and the
reheat delta T.
Note that PVAVS and VAVS do not necessarily deliver the minimum
supply air temperature specified. This may skew the relative
gas/electricity heating energy results one expects.
At 01:03 PM 14/06/2012, John Aulbach wrote:
>If I am not correct, you would enter the reheat delta T at the
>SYSTEM level. Try that.
>
>John Aulbach
>Partner Energy
>
>
>From: "Pasgar, Arash" <APasgar at dbrinc.com>
>To: "equest-users at lists.onebuilding.org" <equest-users at lists.onebuilding.org>
>Sent: Tuesday, June 12, 2012 7:58 AM
>Subject: [Equest-users] VAV with electric heat coil
>
>Hi All,
>
>I am trying to model a package roof top VAV unit with electric heat coil.
>
>At system level heating I selected:
>
>System type: Pkgd Var Val
>Heat source: furnace
>Zone heat source: Electric (each zone has a VAV with electric heat
>coil, EAT=55, LAT=85)
>Heating capacity:-220 MBH (same as my mech sch. For RTVAV)
>
>At zone level I think I have to enter heating capacity or reheat
>delta T, but both of them are n/a.
>How can I get this one fix?
>
>On my previous model, I modeled the electric heat coil as a
>baseboard in each zone!!!
>I am not sure if I did it correctly because at the end my space
>heating on baseline was very low compare to proposed and made energy
>saving percent equal to -97%.
>
>Thanks in advance for your help
>
>
>Arash Pasgar
>Mechanical Designer
>
>Description: Description: Description: Description: Description
>
>
>v. 210.546.0200 | <http://www.dbrinc.com>www.dbrinc.com
>
>
>_______________________________________________
>Equest-users mailing list
><http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>To unsubscribe from this mailing list send a blank message to
><mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>
>_______________________________________________
>Equest-users mailing list
>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>To unsubscribe from this mailing list send a blank message to
>EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>
Christopher Jones, P.Eng.
Suite 1801, 1 Yonge Street
Toronto, ON M5E1W7
Tel. 416-203-7465
Fax. 416-946-1005
email cj at enersave.ca
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120614/579c6d17/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 4c9f7ee.jpg
Type: application/octet-stream
Size: 4870 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120614/579c6d17/attachment-0002.obj>
More information about the Equest-users
mailing list