[Equest-users] DOE22 weather processor
Joe Huang
yjhuang at whiteboxtechnologies.com
Tue Jun 19 11:51:35 PDT 2012
Sorry for the repeated partial postings that just occurred. I have no
idea what happened, but it had to do with my mail server, since I just
did a single "send".
On 6/19/2012 11:48 AM, Joe Huang wrote:
> This is true. Unless the DOE-2 weather processor (doewth, wth.f) has
> been upgraded for DOE-2.2, it is not Y2K compliant (nor is DOE-2.1X
> itself, for that matter). What I've been doing for years has been to
> reset the years > 20XX to 19XX. Please note that this does not affect
> the contents of the weather file at all. Other deficiencies in the
> DOE-2 weather processor and format are:
> 1) fails at latitudes > 62.5 or < -62.5, i.e., above the Arctic or
> below the Antarctic Circles because the routine for determining
> sunrise fails.
> 2) temperatures and solar radiation are stored in integer F or
> BTU/hr-ft2, wind direction in octals, wind speed in 0.1 knots, etc.,
> causing round-off errors
> especially when the input weather data are in SI units.
> I've made numerous changes to the DOE-2 weather processor to overcome
> these limitations, while keep the file format compatible with the
> original DOE-2 *.BIN format, but minor changes would also be needed in
> doesim to access or read these enhancements, but I haven't made any
> effort to promote such changes.
>
> Joe
>
> Joe Huang
> White Box Technologies, Inc.
> 346 Rheem Blvd., Suite 108D
> Moraga, CA 94556
> (o) (925)388-0265 (c) (510)928-2683
> www.whiteboxtechnologies.com
> "Building energy simulations at your fingertips"Joe Huang
>
>
> On 6/19/2012 7:25 AM, Jonathan Bowser wrote:
>> I don't know if this helps, but maybe it'll spark a thought by
>> someone on here...
>>
>> I've recently played with the DOE-2 Processor for weather
>> conversion. I was rummaging around the source code and found
>> comments in the code that basically stated one of the algorithms for
>> computing information that is dependent on the earth's position about
>> the sun were only valid between the time between March 1, 1900 and
>> December 31, 1999 for time zones east of the international date line.
>>
>> Why is that the case? I don't really know, but maybe someone else
>> can chime in and provide some insight on a workaround for you.
>>
>> -- Jon
>>
>>
>> -----Original Message-----
>> From: equest-users-bounces at lists.onebuilding.org
>> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
>> Chris Jones
>> Sent: Tuesday, June 19, 2012 9:08 AM
>> To: equest-users at lists.onebuilding.org
>> Subject: [Equest-users] DOE22 weather processor
>>
>> I am making a TRY weather file for 2011.
>>
>> The INP file doesn't like dates above 1999.
>> PACK
>> TRY Vancouver -999
>> TRY 71892 -999 8 49.18123.1830-BITNORMAL 4 20. .025
>>
>> I can use -999 and it works but if I put 2011 the processor quits and
>> tells me:
>> --- ERROR --- YEAR IS OUTSIDE ALLOWED RANGE. THE ALLOWED
>> RANGE IS -1 TO 1999. PROCESSING WILL BE TERMINATED.
>>
>> Any ideas?
>>
>>
>> >>
>> Christopher Jones, P.Eng.
>> Suite 1801, 1 Yonge Street
>> Toronto, ON M5E1W7
>> Tel. 416-203-7465
>> Fax. 416-946-1005
>> email cj at enersave.ca
>>
>> _______________________________________________
>> Equest-users mailing list
>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>> To unsubscribe from this mailing list send a blank message to
>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>> _______________________________________________
>> Equest-users mailing list
>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>> To unsubscribe from this mailing list send a blank message to
>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>
>
--
Joe Huang White Box Technologies, Inc. 346 Rheem Blvd., Suite 108D
Moraga, CA 94556 (o) (925)388-0265 (c) (510)928-2683
www.whiteboxtechnologies.com "Building energy simulations at your
fingertips"
More information about the Equest-users
mailing list