[Equest-users] Equipment Tab
Dahlstrom, Aaron
ADahlstrom at in-posse.com
Fri Mar 9 07:21:14 PST 2012
Omar -
I generally only use the "Internal Energy Sources" for gas loads in the space (eg cooking appliances) or for process heat gains that are not derived from a meter (eg heat gain from a baking product that was baked in a different zone and is cooling off in this zone).
As much as I can, I try to total ALL the process electrical sources in a space and assign the wattage and the schedule to match, within the Electrical Equipment schedule. "simple as possible but no simpler."
Of the items that you mentioned - PC's, Printers,electric socket for each workstation, 80 L capacity electric water heater for each WC, Refrigerator, coffee machine - I would put all except the water heater in the Electrical Equipment schedule.
The water heater is a regulated load, not a process load, so that should be defined explicitly and accounted for separately.
As per the help file for "Internal Energy Sources" "Schedule" - "Takes the U-name of the schedule (with TYPE=MULTIPLIER) for any source of internal energy (such as process equipment within a space) other than people, lights, or electrical equipment. Schedule values are fractions of SOURCE-POWER. If SOURCE-SCHEDULE is not entered, the schedule values will default to zero and no source loads are simulated."
Hope this helps!
Aaron Dahlstrom , PE, LEED(r) AP
In Posse - A subsidiary of AKF| 1500 Walnut Street, Suite 1414, Philadelphia, PA 19102
d: 215-282-6753| m: 267-507-5470| In Posse: 215-282-6800| AKF: 215-735-7290
e: ADahlstrom at in-posse.com | in posse web: www.in-posse.com<http://www.in-posse.com/> | akf web: www.akfgroup.com<http://www.akfgroup.com/>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Omar Osama
Sent: Thursday, March 08, 2012 5:43 AM
To: equest
Subject: [Equest-users] Equipment Tab
Dear all,
I've become so confused about the 25% of the process loads, which do count when I place my loads in the "Internal Energy Sources" space, under the Equipment tab in eQuest. I'll brief my confusion in the following question:
1. What loads should I count as "Equipment" and what loads should I count as "Internal Energy Sources" .. knowing that I have an office building with:(PC's, Printers,electric socket for each workstation, 80 L capacity electric water heater for each WC, Refrigerator, coffee machine) ... Knowing that the "Internal Energy Sources" is constrained by eQuest (don't know why) to have only one item with one schedule. which means that only one item of the above-mentioned items should cover the 25% of the total energy costs.
Any contribution to that will be highly appreciated,
Thanks for consideration,
Omar AlRawi
Project Engineer,
EA Sustainable Building Consultants
www.ea-buildingconsultants.com<http://www.ea-buildingconsultants.com/>
________________________________
This e-mail may contain information that is confidential, privileged or otherwise protected from disclosure. If you are not an intended recipient of this e-mail, do not duplicate or redistribute it by any means. Please delete it and any attachments and notify the sender that you have received it in error. Unintended recipients are prohibited from taking action on the basis of information in this e-mail. E-mail messages may contain computer viruses or other defects, may not be accurately replicated on other systems, or may be intercepted, deleted or interfered without the knowledge of the sender or the intended recipient. If you are not comfortable with the risks associated with e-mail messages, you may decide not to use e-mail to communicate with In Posse.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120309/a995209a/attachment-0002.htm>
More information about the Equest-users
mailing list