[Equest-users] Unmet Hours
John Aulbach
jra_sac at yahoo.com
Fri Mar 16 08:07:08 PDT 2012
Matt:
I will look at your run later. But for the VAVs, make sure your thermostats are reverse acting, then increase the deadband to 4 or even 6 deg F.
John Aulbach
Partner Energy
________________________________
From: Matt Clough <mclough at kme-inc.com>
To: "equest-users at lists.onebuilding.org" <equest-users at lists.onebuilding.org>
Sent: Friday, March 16, 2012 8:00 AM
Subject: [Equest-users] Unmet Hours
All right Folks,
It’s time to do that thing again where we talk about unmet hours. I’ll give a little background first: I’m new to equest and to the HVAC industry, so bear with me. The project is a 1F school building (pre-k) with a clerestory, split into 10 zones and predominantly served by series VAV terminals using chilled water and hot water loops. It’s in Houston ,
TX so and are no economizers. I’ve spent the majority of the past few days reading previous discussions and trying a variety of changes. I have attached the INP and PD2 for convenience.
I initially tried to represent the system based on the mechanical/electrical schedules, but that yielded many unmet hours (99%), so it is currently set to auto-size, but am still at about 600 unmet hours (7%). 7 of the zones are series VAV, 2 are single-zone with reheat, and one is a packaged single zone for the MDF room.
* Changing to an auto-sized system provided a large reduction in UH.
* am trying to not manipulate the data by adjusting the cooling/heating ratio.
* The setpoints are 75c/72h. I tried changing them a few degrees in either direction, but did not get a large enough reduction.
* have the fans cycling at night (no OA), which did help reduce the hours
* switched into DDE and set actual CFM from the mechanical plans. This resulted in an increase
As I am looking through the LS-B report, it seems like some of my zone loads might be a little high with some of the heat generation loads at about 12kbtu/h. I think my inexperience hampers my ability to troubleshoot some of the problems because I don’t necessarily have a good sense for what a reasonable result/prediction is.
I appreciate any assistance on this matter and am open to suggestions as far as proper modeling techniques and troubleshooting methods.
Sincerely,
Matt Clough
Mechanical Designer
KME Engineering
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120316/adbf2807/attachment-0002.htm>
More information about the Equest-users
mailing list