[Equest-users] Condensing Boiler in DHW Loop
Bishop, Bill
bbishop at pathfinder-ea.com
Wed May 2 08:27:47 PDT 2012
John,
You could also model a condensing DHW boiler as any other gas DHW heater, but with a custom HIR-FPLR performance curve and a better full load HIR. Part load efficiency is published for several models of condensing DHW boilers. Remember to normalize the custom performance curve to 1.0 at full load.
Regards,
Bill
[cid:image004.png at 01CD2856.45FB2D80]<mailto:wbishop at pathfinder-ea.com>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nick Caton
Sent: Wednesday, May 02, 2012 9:51 AM
To: John Aulbach; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Condensing Boiler in DHW Loop
Hi John,
This may get you started:
- Create a HW Loop
- Create a Condensing Boiler/Pump, attach to the new loop
- Define a process load + schedule in the second tab of the loop to match your DHW consumption. You may need to define the load with MBtu/h and not gpm.
- As a result you should see your condensing DHW pop up in the consumption reports as a green process load on the gas side.
- You might want to leave your normal DHW loop in operation while setting this up as a check to see that you're matching well before deleting. Review the HW loop/boiler inputs carefully to ensure everything is appropriate to DOMHW.
Screengrabs follow to illustrate the concept:
[cid:image005.png at 01CD2856.45FB2D80]
[cid:image006.png at 01CD2856.45FB2D80]
Best of luck!
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John Aulbach
Sent: Tuesday, May 01, 2012 7:00 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Condensing Boiler in DHW Loop
Any suggestions as to how to make the DHW heater a condensing boiler ?? The Condensing feature is for a boiler , which wants a Hot Water loop, NOT a DHW loop..
John R. Aulbach, PE, CEM
Senior Energy Engineer
________________________________
Partner Energy
2154 Torrance Blvd, Ste. 100, Torrance, CA 90501
W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745
www.ptrenergy.com<http://www.ptrenergy.com/> | jaulbach at ptrenergy.com<mailto:|%20jaulbach at ptrenergy.com>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120502/542c6d9f/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 21646 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120502/542c6d9f/attachment-0006.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 73078 bytes
Desc: image005.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120502/542c6d9f/attachment-0007.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 66651 bytes
Desc: image006.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120502/542c6d9f/attachment-0008.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image007.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120502/542c6d9f/attachment-0002.jpg>
More information about the Equest-users
mailing list