[Equest-users] Large model crashes on changing system
Nick Caton
ncaton at smithboucher.com
Wed May 16 15:02:30 PDT 2012
Hi RK,
Your questions are most quickly answerable in reverse order:
#2: yes, you can create a partial model and import into another. I have attached a guide to this approach (also findable within the mailing list archives and elsewhere on the web).
#1: You could take an approach using what you proposed for #2, but I would first try to define your middle stories as single-story shells with no ceiling or floor (adiabatic) and then assigning an appropriate shell multiplier at the first DD shell wizard screen to get the quantities right. That should avoid the whole top/middle/bottom thing.
I also suspect sheer size to be the foundation of your troubles, with geometry-induced errors following close behind.
If you're still stuck I would look hard at whether there's any means to simplify how your 74k windows are defined and/or the associated perimeter wall geometries. To that end I've also attached a previous discussion where a window/wall geometry error was causing crashes in a large model - might be instructive/helpful for your current situation.
Hopefully the above suggestions will simplify things back into working order, but if not it is sometimes productive to save a dummy copy of your file and you'll find removing a specific shell or system will return the model to stability, in which case re-creating the offending item can be faster than trying to ferret out the actual cause. If you take this approach try to work backwards from the point you first noticed issues.
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of rubu98 at gmail.com
Sent: Wednesday, May 16, 2012 3:09 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Large model crashes on changing system
Hello everyone,
This is my first post to this forum - have been using eQuest for a few months now, having used VisualDOE for a few years. I am modeling a large building (about 50 stories, with 21 different shells), and currently I have one system per floor (34 systems total). However, when I try to change the system type for even one system, eQuest crashes. Also, every time I go into DD Wizard to simplify my model and exit the wizard, I would get an "Unhandled Exception" error and eQuest would crash again. Besides, I have about 74,000 windows in the model too.
It'd be great if someone could point out what is wrong with the limited information I can explain above, but to resolve my issue, I am considering alternative solutions and would appreciate if you guys can comment on them:
1. Is there a way to avoid creating Top, Middle and Bottom floors for multiplied floors and have only one floor? Cutting down on two extra floors for every shell with mutipliers might help.
2. Is there a way to split up the model into two, enter all inputs seperately and then import one model into another to complete the model and run the simulations? I know this sounds complicated, but would appreciate some pointers from people who have successfully tried this before.
Thanks,
RK.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120516/4f7c41c2/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120516/4f7c41c2/attachment-0002.jpg>
-------------- next part --------------
An embedded message was scrubbed...
From: Nick Caton <ncaton at smithboucher.com>
Subject: [Equest-users] eQuest importing mini-gude
Date: Tue, 12 Oct 2010 20:32:17 +0000
Size: 227835
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120516/4f7c41c2/attachment-0004.eml>
-------------- next part --------------
An embedded message was scrubbed...
From: "Chueh, James" <james.chueh at siemens.com>
Subject: RE: [Equest-users] Change of window parameter cannot be saved in Wizardmode
Date: Thu, 8 Sep 2011 02:13:10 +0000
Size: 91474
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120516/4f7c41c2/attachment-0005.eml>
More information about the Equest-users
mailing list