[Equest-users] Building area method ASHRAE 90.1
Patrick J. O'Leary, Jr.
poleary1969 at gmail.com
Wed May 23 14:36:55 PDT 2012
and maria is correct "Space by space method does allow trade-offs
between spaces, because it compares the total specified lighting wattage
for the entire building to the _sum_ of space-by-space allowances (see
section 9.6.1 d)." this is also noted in the user's manual in example 9-p.
On 5/23/12 2:09 PM, Maria Karpman wrote:
>
> Patrick,
>
> I agree with Bill that it is irrelevant for energy modeler whether
> space-by-space or building area method was used to document compliance
> of the lighting design with the energy code (see his discussion on
> mandatory versus prescriptive requirements of 90.1). As a side note,
> when compliance with energy code is documented using prescriptive path
> (for example via ComCheck), exceeding LPD allowances for individual
> space types does not mean that project fails to comply using
> space-by-space method, as you seem to imply below. Space by space
> method does allow trade-offs between spaces, because it compares the
> total specified lighting wattage for the entire building to the _sum_
> of space-by-space allowances (see section 9.6.1 d). I also agree with
> Bill that space-by-space method is the only way to provide meaningful
> feedback to the design team. It also helps to catch issues with LPD
> calculations, such as treating partial or temporary lighting in core
> and shell spaces as complete lighting system, or failing to include
> unspecified plug-in lighting in hotels into LPD calculations.
> Space-by-space method also comes with a carrot of increased lighting
> allowances as described in 9.6.2.
>
> Maria
>
> *From:*equest-users-bounces at lists.onebuilding.org
> [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of
> *Patrick J. O'Leary, Jr.
> *Sent:* Wednesday, May 23, 2012 3:41 PM
> *To:* Bishop, Bill
> *Cc:* eQuest Users; Oscar B.
> *Subject:* Re: [Equest-users] Building area method ASHRAE 90.1
>
> referencing this comment: "The only obvious case for using the
> Building Area Method to determine modeled LPD is the case that Nick
> mentioned where lighting neither exists nor is specified."
>
> or when the lighting designer/electrical engineer has higher lighting
> densities that exceed one (or more) of the space-by-space maximum
> allowable lpds but compensates for it by having lower lpds in other
> spaces such that the whole building lpd does not exceed the maximum
> allowable by the whole building method.
>
>
>
>
> On 5/23/12 7:45 AM, Bishop, Bill wrote:
>
> Building Area and Space-by-Space are not methods for designing
> lighting systems. They are prescriptive requirements for demonstrating
> lighting energy compliance in 90.1. The LPD allowances in Tables 9.5.1
> and 9.6.1 do not need to be complied with if using energy modeling to
> demonstrate compliance for 90.1 and for LEED. (Only the Mandatory
> Provisions of 9.4 need to be met for the lighting design.) Energy
> modelers only need to know the lighting power and space use
> categorizations of the design as shown on the drawings (along with
> schedules and controls), not the process used to design it (which
> typically considers light levels in footcandles or lux).
>
> I think that /if/ a lighting system has been designed, a strong
> argument can be made that the space-by-space method needs to be used
> in both the proposed and baseline cases, and that lighting power needs
> to be entered individually for each space/zone.
>
> "If construction documents are complete, the proposed
> building lighting system power is modeled as shown on the design
> documents." (ASHRAE 90.1 User's Manual, p. G-17)
>
> "The LPD for the proposed design is taken from the design documents
> for the building. The LPD specified in the models must correspond to
> the spaces within each thermal block." (ASHRAE 90.1 User's Manual, p.
> 11-14 and also p. G-18)
>
> The only obvious case for using the Building Area Method to determine
> modeled LPD is the case that Nick mentioned where lighting neither
> exists nor is specified.
>
> As Maria Karpman, Nick and Patrick have mentioned, you are likely to
> show higher energy savings using the Space-by-Space method. Beyond
> that, using Space-by-Space allows you to give valuable feedback to the
> design team, which I would argue is a responsibility of energy
> modelers. It is routine for me to point out areas of potential
> improvement of the lighting design in every project I model, based on
> the allowances in Table 9.6.1. "Yes, Ms. Architect, that is a lovely
> looking light fixture, but 2.6 W/ft2 of lounge lighting is more than
> twice the baseline allowance." I don't know how you give helpful
> feedback if you are just comparing two building-averaged lighting
> power densities.
>
> Regards,
>
> Bill
>
> ** <mailto:wbishop at pathfinder-ea.com>
>
> *From:*equest-users-bounces at lists.onebuilding.org
> <mailto:equest-users-bounces at lists.onebuilding.org>
> [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of
> *Patrick J. O'Leary, Jr.
> *Sent:* Tuesday, May 22, 2012 7:28 PM
> *To:* Nick Caton
> *Cc:* eQuest Users; Oscar B.
> *Subject:* Re: [Equest-users] Building area method ASHRAE 90.1
>
> actually nick, i agree with you. since i don't design lighting
> systems i always ask the lighting designer which method they're using
> before i start building a model. almost all of the lighting
> designer's i've worked with use the whole building area method, though
> as you point out the space-by-space method can actually do a bit
> better for energy savings.
>
> my point is that there isn't a mandate to use either the
> space-by-space or whole building area method and there is no
> justification as far as 90.1-200x is concerned for a usgbc reviewer to
> claim that the space-by-space method be used. the requirement per
> 90.1 is that the method be consistent in both the proposed and
> baseline models. space-by-space in both or whole building in both.
> this is what i've had to point out to reviewer's when i've received
> comments. just quote chapter & verse to show that the method
> (space-by-space or whole building) used meets the 90.1 app g
> requirement and is applied the same in both models.
>
> as far as comcheck, comcheck reports from lighting designers are only
> as good as the individual filling them out. i've had lighting
> designers (with all of their extra letters including pe after their
> names) fill them out incorrectly. i.e. not having all the lighting
> fixtures the same in drawing schedules as input into comcheck, not
> having same number of fixtures in drawings and in comcheck, not having
> the same floor areas in drawings and in comcheck, and worst of all,
> not using the same methodology in comcheck that they've used to design
> the lighting system in the first place. yes, i've seen comcheck
> reports that indicate space-by-space when the lighting designer has
> told me whole building method. and vice versa. so i always end up
> confirming my lighting take-offs (from the lighting plans) and
> methodology with the lighting designer/electrical engineer and their
> comcheck report.
>
> On 5/22/12 3:58 PM, Nick Caton wrote:
>
> Hmm, I think I'm on the fence here.
>
>
> My practice is identical to Vikram's description for both energy
> modeling and when documenting compliance for my lighting designs:
> Choose whatever method you wish, but always use the same approach for
> baseline and proposed. This is pretty clear outside of Appendix G,
> when documenting compliance. For modeling, I don't use either
> approach predominantly -- it depends on the project.
>
> Since Patrick is pushing one side, I'll play devil's advocate =): I
> can affirm I've used "whole building" averaged LPD in proposed models
> for successful LEED submission without incident multiple times,
> documenting that clearly along the way, but I was using "whole
> building" for the baseline as well in each instance. I do not
> personally read 90.1 or LEED to explicitly require LPD be defined with
> space-by-space for a proposed model. Patrick, I just checked each of
> your citations and the only specific call for either method is when
> the lighting system has not been designed, in which case the whole
> building approach is prescribed. Keep in mind both methods should sum
> to the same total installed watts for the proposed design.
>
> Back to the neutral perspective: I'll emphasis I do use both approaches.
>
> To Oscar's case: My general experience has been the whole building
> method is less generous in net allowable watts when you run the
> numbers both ways. In other words, you may stand to earn more LEED
> points by making your baseline more detailed, using space by space.
> My suggestion for Oscar is to simply go with the reviewer's flow and
> possibly walk away with another point tucked under your arm... it'll
> probably be a similar amount of effort on your part relative to
> composing an opposing response, and you won't have to worry about the
> reviewer disagreeing =).
>
> I agree space-by-space is 'better' for that reason alone -- if
> different at all, it tends to yield a better performance rating. I
> will acknowledge space-by-space is also "more accurate," notably so if
> you're simultaneously defining distinct & accurate lighting schedules
> space-by-space, but whether the corresponding additional time
> investment and resulting "accuracy boost" are advantageous for a given
> LEED model is a toss-up. I personally feel the role accuracy plays in
> a LEED model is often overblown to a point of silliness, but that's a
> personal call we each need to make and a whole 'nother discussion.
>
> Hot related tip: energy modelers and MEP designers alike need to be
> aware of COMcheck. I find it an invaluable time saver for speeding up
> takeoffs for whole bldg & space by space calcs, and it's only as
> costly as eQuest.
>
> ~Nick
>
> cid:489575314 at 22072009-0ABB
>
> **
>
> *NICK CATON, P.E.*
>
> SENIOR ENGINEER
>
> Smith & Boucher Engineers
>
> 25501 west valley parkway, suite 200
>
> olathe, ks 66061
>
> direct 913.344.0036
>
> fax 913.345.0617
>
> www.smithboucher.com__
>
> *From:*equest-users-bounces at lists.onebuilding.org
> <mailto:equest-users-bounces at lists.onebuilding.org>
> [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of
> *Patrick J. O'Leary, Jr.
> *Sent:* Tuesday, May 22, 2012 4:49 PM
> *To:* Sami, Vikram
> *Cc:* eQuest Users; Oscar B.
> *Subject:* Re: [Equest-users] Building area method ASHRAE 90.1
>
> as long as a lighting system has been designed:
>
> according to ashrae/appendix g the uniform/whole building method
> applies a uniform lpd to the BASELINE building only while the PROPOSED
> uses what is designed - so long as the design is based on the whole
> building area method. the lpd of the PROPOSED design should not be
> applied uniformly to the PROPOSED building simulation.
>
> see appendix g, table g3.1, section 6 lighting, subsection b, page 173
> (2004), page 179 (2007). user's manual pages g-17/18 (2004 & 2007)
>
> i would suggest to quote table g3.1 when replying to the reviewer's
> comment. i have had reviewer's tell me i have to use the
> space-by-space method in a simulation for both proposed and baseline
> buildings. this is not correct. what is correct is that the
> simulation reflect the methodology used by the lighting designer. if
> the lighting design is based on the whole building method then the
> whole building method maximum lpd is used in the BASELINE building.
> if the design is based on the space-by-space method then the
> space-by-space maximum lpd for each space type is used in the BASELINE
> building. in either case the PROPOSED building should reflect what is
> designed. by 'what is designed' i mean look at the lighting plans,
> lighting schedules, and enter the lpd for each space/zone (thermal
> block) based on the number of fixtures, watts per fixture, and square
> feet of space.
>
>
>
> On 5/22/12 2:15 PM, Sami, Vikram wrote:
>
> The building area method applies a uniform LPD to the entire building.
> If you do that in your baseline, you need to apply a uniform LPD to
> you proposed building too.
>
> In general, I don't recommend using the building are method -- the
> space by space method is a better approach.
>
> **
>
> *Vikram Sami*, LEED AP BD+C
>
> Sustainable Design Analyst
>
> 1315 Peachtree St. NE, Atlanta, GA 30309
>
> t: 404-443-7462 f: 404.892.5823 e: vikram.sami at perkinswill.com
> <mailto:vikram.sami at perkinswill.com> www.perkinswill.com
> <http://www.perkinswill.com/>
>
> *Perkins+Will.*Ideas + buildings that honor the broader goals of society
>
> *From:*equest-users-bounces at lists.onebuilding.org
> <mailto:equest-users-bounces at lists.onebuilding.org>
> [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of
> *Oscar B.
> *Sent:* Tuesday, May 22, 2012 4:38 PM
> *To:* eQuest Users
> *Subject:* [Equest-users] Building area method ASHRAE 90.1
>
> How does the building area method work?
>
> I just got a comment from the review team for a project pursuing LEED
> certification.
>
> I used the building area method for the baseline case and in the
> proposed case I put the LPD from the lighting design. However they
> told me that the same method has to be used in both cases.
>
> Any help would be appreciate.
>
>
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message toEQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120523/0ad57b67/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 21646 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120523/0ad57b67/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120523/0ad57b67/attachment-0002.jpeg>
More information about the Equest-users
mailing list