[Equest-users] Regarding multiple floors in a building

bfountain at greensim.com bfountain at greensim.com
Thu May 24 05:25:18 PDT 2012


On the footprint shape screen of the wizard (screen 2 of the DD shell wiz), if your floor-to-ceiling height is more than a foot lower than your floor-to-floor height, eQUEST will create a plenum space.  Whether it creates a single plenum for the floorplate or a plenum per zone depends on whether you HVAC system is ducted or plenum return.

I suspect you may be looking at the 3d view where ceiling partitions are turned off by default but they will still be shown on the component tree.
Brian Fountain
bfountain at greensim.com

-----Original Message-----
From: mayank bhatnagar <mayank.23aug at gmail.com>
Sender: equest-users-bounces at lists.onebuilding.org
Date: Thu, 24 May 2012 09:48:41 
To: <equest-users at lists.onebuilding.org>
Subject: [Equest-users] Regarding multiple floors in a building

_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG



More information about the Equest-users mailing list