[Equest-users] 90.1 App G Fan Power and EER Calculations
Maria Karpman
maria.karpman at karpmanconsulting.net
Thu May 31 08:35:34 PDT 2012
Nick, Steve and Paul,
I believe that using ARI fan power in EIR calculations is the way to go,
because the efficiency tables in 90.1 Section 6 show the required
performance at ARI conditions (see the last column in each table), not at
the project conditions. Here is the related abstract from 90.1 Section 6:
6.4.1.1 Minimum Equipment EfficienciesListed
EquipmentStandard Rating and Operating Conditions.
Equipment shown in Tables 6.8.1A through 6.8.1G shall have
a minimum performance at the specified rating conditions
when tested in accordance with the specified test procedure.
When a packaged system that meets 90.1 efficiency requirements at ARI
conditions is installed in a project where the fan power is higher than in
ARI testing procedure (e.g. projects with more extensive ductwork, air
filters, energy recovery, etc.), it will have a lower actual EER than whats
listed in Section 6. However, this wouldnt make the installation
incompliant with mandatory efficiency requirements in 90.1 Section 6. In my
experience, LEED reviewers do comment on EIR calculations if EIR is not what
they expect. However, using Appendix G fan power in baseline EIR
calculations typically results in a more stringent baseline (lower EIR), so
they do not insist on changing it.
Thanks,
Maria
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nick Caton
Sent: Thursday, May 31, 2012 9:56 AM
To: Paul Riemer; Steve Burley; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] 90.1 App G Fan Power and EER Calculations
Hi Paul!
I maintained the exact same position for a long while, though I thought I
was the vocal minority =)! Ultimately, you can argue for/against either
approach as having different advantages of correctness. Ive heard future
addenda or versions of 90.1 may address the conundrum by stipulating
something more simplistic than either approach, like a uniform factor to
come up with compressor/condenser energies from the total consumption.
My final position is both approaches make sense, and for different reasons
modelers should use whichever they feel most comfortable defending should
their methodology come into question. My LEED reviewers have to this point
taken zero interest in which approach Ive used in my calculations, after
using both, so I take it this degree of nuance is probably not on their
usual checklists. Ive switched over to the ARI approach for a few reasons,
but not because I feel a Pfan-based approach is wrong.
Best wishes,
~Nick
cid:489575314 at 22072009-0ABB
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: Paul Riemer [mailto:Paul.Riemer at dunhameng.com]
Sent: Thursday, May 31, 2012 7:29 AM
To: Nick Caton; Steve Burley; equest-users at lists.onebuilding.org
Subject: RE: 90.1 App G Fan Power and EER Calculations
Nick, Steve, and list,
I think I concur more with Steve. If you use Nicks approach to calculate
the cooling EIR by subtracting out ARI rated fan power from the 90.1 EER AND
then model the 90.1 fan power limits directly, you will be modeling a
packaged unit that does not comply with the package EER.
I could see using other splits of fan and cooling, but a baseline model
should comply with both limits.
Paul Riemer, PE, LEED AP BD+C
DUNHAM
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nick Caton
Sent: Tuesday, May 29, 2012 10:51 AM
To: Steve Burley; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] 90.1 App G Fan Power and EER Calculations
Steve,
There are two schools of thought for dealing with fan power in cooling
efficiency calcs. The first pulls away the baseline fan power Pfan, as
youre describing, and the other instead pulls out a fan energy draw based
on ARI testing procedures
400 CFM/ton à 365W/1000CFM. I follow the latter
these days, but see both as viable.
The two approaches result in similar results when your Pfan calculation
doesnt involve a lot of static pressure adders. When it does, the
approaches diverge in a fashion that may be either problematic or helpful in
a LEED rating sense. Attached discussion sums up things further, includes
an outline of an ARI-based approach. You can find more discussions and read
into advantages/disadvantages to both approaches in the mailing list
archives.
That said, I havent checked your math or references but the procedure
youve roughly outlined sounds alright for a Pfan approach. There are steps
in between what youve written for correctly coming up with Pfan, but I take
it thats implicit.
~Nick
cid:489575314 at 22072009-0ABB
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Steve
Burley
Sent: Tuesday, May 29, 2012 6:37 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] 90.1 App G Fan Power and EER Calculations
Im sure this must have been asked before but I cannot find an answer in the
archives if there is one please point me to it.
I have interpreted the requirements of 90.1, App. G to split the EER of
cooling equipment with a supply fan into its components to model the fan
energy separately as follows:
1. Say a space has a cooling load of 80,000Btu/h and the system is
packaged single zone, EER 11.2.
2. Calculate airflow for 20°F temperature difference 3708cfm
3. Calculate fan bhp from Table G3.1.2.9 3.49bhp
4. Calculate fan power as per G3.1.2.9 2972W
5. Calculate gross input power from load and EER 7143W
6. Subtract 4 from 5 for compressor/condenser input power 4171W
7. Convert to EIR 0.1779
This appears to make sense from reading App. G but ends up with high fan
power consumption and low space cooling loads. Am I wrong here?
Thanks,
Steven Burley
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120531/49ec0d22/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120531/49ec0d22/attachment-0002.jpeg>
More information about the Equest-users
mailing list