[Equest-users] VRF in eQuest and LEED
Gastón Michaud F.
gaston.michaud at cts-cr.com
Mon Nov 26 15:32:29 PST 2012
Thank you Paul for your response.
I did not model custom curves, I understand that if a use the PVVT system and set the compressor to variable speed, there is no need to modify them; am I correct? If that is the case, I’ll try to model the custom performance curves; I was just trying to avoid that since I haven’t been able to get the manufacturer information…
Do you think the LEED reviewers would accept this approximation without the custom curves? I’ve read before that not using the curves gives a conservative result, which I am willing to accept.
Thanks!
Ing. Gastón Michaud F.
Tel.: (506) 2222-7529
Fax: (506) 2256-5608
From USA: 1-305-433-3668
Calle 30, Avenida 0 y 2. San José, Costa Rica
[Description: Description: Description: Description: LEEDAP_BDCbw]
[Description: Logo CTS firma]
Este correo puede contener información protegida por el secreto profesional. Si usted no es la persona a quien va dirigido, por favor tome en cuenta que su divulgación, distribución o reproducción es estrictamente prohibida. Cualquier persona que reciba este mensaje por error debe notificarlo inmediatamente al remitente vía telefónica o correo electrónico y borrarlo permanentemente de su computador. Los comentarios plasmados en este correo son del remitente solamente y no reflejan necesariamente la posición de CTS S.A.
Por favor considere su responsabilidad con el medio ambiente antes de imprimir este correo electrónico
----------------------------------------------------------------------------------------------------------------
This mail may contain information that is legally privileged, confidential or exempt from disclosure. If you are not the intended recipient, please note that any dissemination, distribution or copying of this message is strictly prohibited. Anyone who receives this message in error should notify the sender immediately by telephone or by e-mail and delete it permanently from their computer. The opinions above are those of the author and do not necessarily reflect the position of CTS S.A.
Please consider your environmental responsibility before printing this e-mail
From: Paul Diglio [mailto:paul.diglio at sbcglobal.net]
Sent: Monday, November 26, 2012 5:10 PM
To: Gastón Michaud F.; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] VRF in eQuest and LEED
Hello:
I have submitted projects to LEED using the same methodology without any problems. Did you model custom performance curves?
Perhaps you explanation was not clear?
Paul Diglio, CEM, CBCP
87 Fairmont Avenue
New Haven, CT 06513
203-415-0082
www.pdigliollc.com<http://www.pdigliollc.com>
________________________________
From: Gastón Michaud F. <gaston.michaud at cts-cr.com>
To: "equest-users at lists.onebuilding.org" <equest-users at lists.onebuilding.org>
Sent: Mon, November 26, 2012 5:31:19 PM
Subject: [Equest-users] VRF in eQuest and LEED
Hello everyone,
We are applying for a LEED certification in a project which includes a VRF system in several areas. In order to model such system, we followed the methodology described in the document “Energy Trust of Oregon”; and submitted an explanation to the LEED reviewers describing each step taken in eQuest. We got the following review comment:
“The simulation software used is not capable of modeling VRF systems. The project team has not provided information describing how the VRF systems performance has been modeled to reflect the actual design. Please provide a narrative and any supporting documentation demonstrating that the VRF system characteristics have accurately modeled.”
Has anyone had any similar issue regarding a LEED project? After reading their comment, it seems that they might have overlooked our explanation, or maybe it was just not enough. Any ideas? Does LEED accepts this approximation? Thank you very much!
Ing. Gastón Michaud F.
Tel.: (506) 2222-7529
Fax: (506) 2256-5608
From USA: 1-305-433-3668
Calle 30, Avenida 0 y 2. San José, Costa Rica
[Description: Description: Description: Description: LEEDAP_BDCbw]
[Description: Logo CTS firma]
Este correo puede contener información protegida por el secreto profesional. Si usted no es la persona a quien va dirigido, por favor tome en cuenta que su divulgación, distribución o reproducción es estrictamente prohibida. Cualquier persona que reciba este mensaje por error debe notificarlo inmediatamente al remitente vía telefónica o correo electrónico y borrarlo permanentemente de su computador. Los comentarios plasmados en este correo son del remitente solamente y no reflejan necesariamente la posición de CTS S.A.
Por favor considere su responsabilidad con el medio ambiente antes de imprimir este correo electrónico
----------------------------------------------------------------------------------------------------------------
This mail may contain information that is legally privileged, confidential or exempt from disclosure. If you are not the intended recipient, please note that any dissemination, distribution or copying of this message is strictly prohibited. Anyone who receives this message in error should notify the sender immediately by telephone or by e-mail and delete it permanently from their computer. The opinions above are those of the author and do not necessarily reflect the position of CTS S.A.
Please consider your environmental responsibility before printing this e-mail
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20121126/218d311d/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 2289 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20121126/218d311d/attachment-0008.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.jpg
Type: image/jpeg
Size: 5466 bytes
Desc: image006.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20121126/218d311d/attachment-0009.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 2289 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20121126/218d311d/attachment-0010.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 5468 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20121126/218d311d/attachment-0011.jpg>
More information about the Equest-users
mailing list