Examine your ERV-TEMP-CTRL setpoint.  If it's set to float you can end up
overshooting your mixed air temperature setpoint and having to recool the
air.

Also, ERV-RUN-CTRL should be set to WHEN-MIN-OA or one of the
OA-EXHAUST-DT/DH options for maximum energy savings.

That being said, eQUEST's ERV algoirthm has never given me good results.
I've had a lot of trouble showing savings and have experienced similar
issues as you describe.

Check your hourly reports for the system.  There are a number of parameters
related to ERV's that you can monitor and check to see if its working as
intended.

[image: Inline image 2]



On Fri, Nov 30, 2012 at 11:59 AM, Andrew Clagett <AndrewC at hargis.biz> wrote:

> Hello all. After finalizing my building and obtaining what appeared to be
> reasonable output, I removed the ERV devices (modeled at 85% efficient
> cross-flow air to air heat exchangers) from the model to ascertain the
> energy savings attributable to those devices.****
>
> ** **
>
> And my total energy consumption went *DOWN* over 6%! Inexplicably, ‘space
> cooling’ and ‘pumps & aux.’ energy consumption has decreased by a  far
> larger amount than ‘space heating’ increased. I would have expected both of
> those values to increase along with the ‘space heating’ energy consumption
> (which did increase).****
>
> ** **
>
> Anyone have any idea why that might be?****
>
> ** **
>
> *Andrew Clagett, *PE, LEED AP ****
>
> Mechanical ****
>
> d |  206.436.0494     o | 206.448.3376    e | andrewc at hargis.biz    v-card<http://www.hargis.biz/vcards/Andrew%20Clagett.vcf>
> ****
>
>  ****
>
> *HARGIS** *****
>
>      mechanical • electrical • telecommunications • security     ****
>
> ** **
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20121130/933e8797/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 10632 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20121130/933e8797/attachment-0002.png>


More information about the Equest-users mailing list