Steven,
Consult the USGBC website and look for the "Treatment of District or Campus Thermal Energy in LEED v2 and LEED 2009" document.  This will guide you how you will end up modeling the baseline systems.
This document does not necessarily cover the baseline pump setup if you go for Option 1.  For my submissions I tend to be conservative and go with the values described in Addendum AI of ASHRAE 90.1 2007.
It may also be useful to your LEED team to find the 2010 LEED Campus App Guide to see if any of the special campus rules apply to other credits.
Hope this helps,
Joe Lewis
Fortier Engineering
Pittsburgh, PA
  ----- Original Message ----- 
  From: Steven Savich 
  To: bldg-sim at lists.onebuilding.org 
  Cc: equest-users at lists.onebuilding.org 
  Sent: Tuesday, October 09, 2012 7:14 PM
  Subject: [Equest-users] LEED NCv2009 - baseline for gymnasium
  All,
   
  I'm at the planning stage for a LEED NC v 2009 compliance model.  The building is a university gymnasium with a main gym and two practice gyms.  The facility also contains locker rooms, a weight room, a sports medicine area, offices, classrooms, and circulation spaces.  The building has two floors above grade, plus a basement mechanical room, with a floor area of roughly 90,000 SF.  Most of the facility is gymnasium space, the other ("non-predominant") uses do not individually total over 20,000SF in area.  The heating source is a campus steam loop fed by a central plant with natural gas-fired steam boilers.  Cooling is by a campus chilled water loop.  Based on G3.1.1 and table G3.1.1A, the required LEED baseline HVAC system will be System 5-Packaged VAV with Reheat - DX cooling and Hot-water fossil fuel boiler.
   
  My read on this is that, for the LEED baseline, I will have two separate system 5's, one for each floor, with a unit heater for the basement mech room.  Since the campus has central heating and cooling, do I use those systems to provide heating & cooling sources for the LEED baseline, or do I use DX cooling  and a hot water fossil fuel boiler per table G3.1.1B?
   
  Thanks in advance.
  Steven 
   
  Steven Savich, LEED AP
  Systems West Engineers
  411 High Street
  Eugene, OR  97401-2427
  (541) 342-7210
  (541) 342-7220 (fax)
   
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20121010/ce71f2ac/attachment-0001.htm>
    
    
More information about the Equest-users
mailing list