[Equest-users] Return Fans
    Bruce Easterbrook 
    bruce5 at bellnet.ca
       
    Mon Oct 29 10:26:17 PDT 2012
    
    
  
You need to exhaust the 1500 CFM.  If you exhaust 1200 eQuest will 
assume there is 300 CFM of return air.  Your model is a box. 
_Everything_ going in or out must balance.  If you don't do it eQuest will.
Bruce Easterbrook P.Eng.
Abode Engineering
On 29/10/2012 12:36 PM, Ömer Moltay wrote:
> Dear All,
>
> I am trying to model a system with 1500 CFM system supply but no 
> return, all of the flow will be exhausted from the zones. Looking at 
> hourly reports, I can never get the return flow to be zero, eQuest 
> will always add exhaust and return and make my system supply 3000 CFM. 
> How does one zero the return flow?
>
> Thanks,
>
> Omer Moltay
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to 
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20121029/7033c190/attachment-0002.htm>
    
    
More information about the Equest-users
mailing list