Hi guys,
 
I'm trying to create chiller part load EIR curves based on manufacturer
data. I have part load (25%, 50%, 75%, 100%) as the independent variables
(X), and part load EIRs as the dependent variable (Z). The part load EIRs
from manufacturer are much better than what I get when I use default EQUEST
curve. But when I run the model and compare with same model with default
curve, my chiller electrical energy consumption is increased significantly
(with the manufacturer data). Has anyone been able to successfully create
performance curves, or does anyone know of any documentation that might
explain how to properly create these curves? Any help is greatly
appreciated.
 
 
Regards,
 
 
Behnam
 
 
-- 
Behnam Jowkar, MASc
Energy Services Associate
 
Fluent Group Consulting Engineers Inc.
295A Broadway Avenue, Second Floor
P.O. Box 188, Orangeville, Ontario, L9W 2Z6
t 888.358.3683 x704  f 866.620.7502  c 519.938.7657
www.fluentgroup.com
 
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20121031/2f03c155/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: EDR_CoolTools_Chiller_Bid_Performance_1.5.zip
Type: application/x-zip-compressed
Size: 299420 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20121031/2f03c155/attachment-0002.bin>
    
    
More information about the Equest-users
mailing list