The USGBC always look for a proof and it won't be as complicated as some
may think, the options you proposed folk will be okay. Incidentally, for
the proposed model do you also use a 1.15 and 1.25 to oversize the cooling
and heating equipments, I saw differernt designers do it differernt
way, and both views were approved by the USGBC at some instances, do you
folks apply the same ratios for the proposed building? thanks in advance
On Wed, Sep 5, 2012 at 11:24 PM, Umesh Atre <umesh at innovativedesign.net>wrote:
> **
> Or another option is a pdf of your input file section that defines the
> sizing ratios.
>
>
> ------------------------------
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Otto
> Schwieterman
> *Sent:* Wednesday, September 05, 2012 4:17 PM
> *To:* Pasgar, Arash; equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] Baseline equipment sizing
>
> I would include print screens of the energy model where you have
> specified the sizing ratio.****
>
> ** **
>
> *From:* Pasgar, Arash [mailto:APasgar at dbrinc.com]
> *Sent:* Wednesday, September 05, 2012 3:35 PM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Baseline equipment sizing****
>
> ** **
>
> Dear all,****
>
> ** **
>
> To size the equipment in baseline, I let the program to size and 25%
> heating oversized and 15% cooling oversized by entering the cool sizing
> ratio 1.15 and heat sizing ratio 1.25.****
>
> ** **
>
> But I have got the following comment:****
>
> ** **
>
> It is unclear whether the Baseline equipment capacities were based on
> sizing runs, and oversized by 25% for heating, and 15% for cooling in
> accordance with Section G3.1.2.2****
>
> ** **
>
> Who can I prove that?****
>
> ** **
>
> Thank you for your kindly help.****
>
> ** **
>
> ** **
>
> *Arash Pasgar
> *Mechanical Designer
>
> [image: Description: Description: Description: Description: Description:
> Description: image001]
>
> v. 210.546.0200 | www.dbrinc.com****
>
> ** **
>
> ________________________________________________________________________________________
> This message contains confidential information and is intended only for the individual or entity named. The use, disclosure, dissemination, distribution, or reproduction of this message by unintended recipients is not authorized and may be unlawful. Please notify the sender immediately by email if you have received this email by mistake and delete this email from your system. Fanning/Howey Associates, Inc. has taken reasonable precautions to see that no viruses are present in the electronic mail. Fanning/Howey Associates, Inc. accepts no liability for any damage caused by any virus transmitted by this email.
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120905/85dd2eda/attachment-0002.htm>
More information about the Equest-users
mailing list