[Equest-users] Building Walls
Bishop, Bill
bbishop at pathfinder-ea.com
Thu Sep 13 06:26:50 PDT 2012
Yes, eQUEST simulates the exterior air film with different hourly values for each exterior surface, based on wind speed and surface roughness. I ran a custom hourly report to verify this for three random exterior walls. If you do this for your own model and scroll down to the yearly summary, you can get a sense of the building-wide average annual value. In the case below, the average value is approximately twice the R-0.17 value included in the ASHRAE 90.1 effective R-values for various exterior constructions. Granted, R-0.35 is small relative to a well-insulated wall, but it can be enough to impact the LV-D reported U-values.
Regards,
Bill
[cid:image001.png at 01CD9190.DD912ED0]
[Senior Energy Engineer 28Jun2012]<mailto:wbishop at pathfinder-ea.com>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bruce Easterbrook
Sent: Wednesday, September 12, 2012 12:47 PM
To: Nick Caton
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Building Walls
As an adder to this the wind speed also varies with the height of the building. The wind speed for a locations weather file is at a standard reference height and would also be adjusted for height of the building.
Bruce Easterbrook P.Eng.
Abode Engineering
On 12/09/2012 12:22 PM, Nick Caton wrote:
I can add a probable bit of method to the madness for those concerned:
The reason exterior air film is not entered as a static property, nor reported lumped in with the constructions' overall assembly U-values, is because it's actually a variable property.
The reference I have handy (Table 5-12, 2001 Fundamentals) lists multiple resistance values for moving air (at various speeds) and still air (for various surface orientations and directions of heat flow).
I take it as implicit that eQuest/DOE2 models this variable contribution from the exterior air film in consideration of the hourly windspeed data available from the weather file, so presenting any single value could be misleading. I've had to make that clarification a few times for those scrutinizing the construction reports without the eQuest detailed simulation reports reference handy ;).
Hope that helps a bit!
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Dahlstrom, Aaron
Sent: Monday, September 10, 2012 4:20 PM
To: Peter Hillermann; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Building Walls
Peter -
We've noticed the identical issue. Another way of stating it - the sequence of layers input for the baseline and the proposed should EXCLUDE contributions from air film. eQUEST adds the interior air film as a separate entry under the Layers tab.
[cid:image004.jpg at 01CD9190.DD912ED0]
ASHRAE's regulations for baseline constructions include the contribution of the exterior air film at a specified windspeed. As far as I can tell, this is how the u-value displayed on the LV-D report is calculated. (Report says "includes exterior air film").
However, we have noticed that the value displayed inside eQUEST as "calculated u-value" does not match the u-value from the LV-D. My theory is that the item shown in eQUEST includes the interior air film but not the exterior air film. (From Vol 2 dictionary, under CONSTRUCTION:U-VALUE - "For exterior surfaces, equals the overall conductance of the surface including the inside air film but excluding the outside air film.")
[cid:image005.jpg at 01CD9190.DD912ED0]
I'm just learning about this issue, so any wisdom from more experienced folks would be welcome!
Aaron
Aaron Dahlstrom , PE, LEED(r) AP
In Posse - A subsidiary ofAKF| 1500 Walnut Street, Suite 1414, Philadelphia, PA 19102
d: 215-282-6753| m: | In Posse: 215-282-6800| AKF: 215-735-7290
e: ADahlstrom at in-posse.com<mailto:ADahlstrom at in-posse.com> | in posse web: www.in-posse.com<http://www.in-posse.com/> | akf web: www.akfgroup.com<http://www.akfgroup.com/>
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Peter Hillermann
Sent: Monday, September 10, 2012 2:02 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Building Walls
To All:
A general piece of information I got from our engineer when we had done the energy model for LEED and something to look out for. He let me know that in the baseline for wall construction to make sure you add in the air film (inside and out) otherwise LEED has an issue with your submission.
Our exact comment was this:
The Baseline Case roof and exterior wall U-values reported in Table 1.4.1A (U-0.048 and U-0.065, respectively) are
inconsistent with the U-values reported in the LV-D report (U-0.054 and U-0.063, respectively). Please ensure consistency
across construction drawings, software summaries, and the EAp2 Template.
Hope it helps.
I also don't know if anyone has this summarized, because I used the baseline walls from this forum that someone had posted and that was the response.
PS: Thank you to this forum, we ended up getting LEED Certified.
Thanks,
PETER HILLERMANN
peterh at westallarchitects.com<mailto:peterh at westallarchitects.com>
westall
architects
3404 pierce drive
chamblee, georgia 30341
o 770.458.4113
c 678.898.2936
westallarchitects.com
[Description: Description: Description: e-signature][Description: Description: Description: USGBC-Logo]
This e-mail may contain information that is confidential, privileged or otherwise protected from disclosure. If you are not an intended recipient of this e-mail, do not duplicate or redistribute it by any means. Please delete it and any attachments and notify the sender that you have received it in error. Unintended recipients are prohibited from taking action on the basis of information in this e-mail. E-mail messages may contain computer viruses or other defects, may not be accurately replicated on other systems, or may be intercepted, deleted or interfered without the knowledge of the sender or the intended recipient. If you are not comfortable with the risks associated with e-mail messages, you may decide not to use e-mail to communicate with In Posse.
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120913/be4d99b6/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 18305 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120913/be4d99b6/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 20869 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120913/be4d99b6/attachment-0010.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120913/be4d99b6/attachment-0011.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 23361 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120913/be4d99b6/attachment-0012.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 23918 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120913/be4d99b6/attachment-0013.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.jpg
Type: image/jpeg
Size: 3221 bytes
Desc: image006.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120913/be4d99b6/attachment-0014.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.gif
Type: image/gif
Size: 2436 bytes
Desc: image007.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120913/be4d99b6/attachment-0002.gif>
More information about the Equest-users
mailing list