Dear Rakesh,
You are correct in the section G 3.1.2.1 it is specified as that Base
case system efficiencies are inclusive of the indoor fan power.
But as per the G3.1.2.4 the supply and return fans shall operate
continuously whenever spaces are occupied and shall be cycled to meet
heating and cooling loads during un-occupied hours . if the supply fan is
modelled as cycling and fan energy is included in the energy – efficiency
rating of the equipment, fan energy shall not be modelled explicitly.
If the above case is not true then you can follow the method specified in
Alternative calculation manual(Ref attached image) to segregate the Fan
power from the total EER if you know the combined EER at a particular dry
bulb and wet bulb temperature(may be even at AHRI condition) having said
that the fan power for all the fans has to be calculated as per the
Table-G3.1.2.9
Hope this helps
<http://www.iesve.com/>
*Vignesh Kumar*
*Senior Project Consultant
LEED Green Associate.
BEE-Energy Auditor.*
T:
+91-7276239991
F:
+44 (0) 141 945 8501
http://www.iesve.com
**Design, Simulate + Innovate with the *<Virtual Environment>***
IES India Pvt. Ltd. Registered in India No. 93090PN2010FTC137424
Registered Office - Dhananjay Plaza,2nd Floor,Plot No.21,
Near Lalani Quntom,Bhavdhan,Pune -411021
Email Disclaimer <http://www.iesve.com/disclaimer.html>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120914/74f88bb4/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: EER.JPG
Type: image/jpeg
Size: 28728 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120914/74f88bb4/attachment-0002.jpeg>
More information about the Equest-users
mailing list