[Equest-users] Fuid-cooler has zero design flow
Pasha Korber-Gonzalez
pasha.pkconsulting at gmail.com
Wed Sep 19 12:00:44 PDT 2012
You might not be able to link these items together (restriction of DOE-2),
you should look in the DOE-2 manuals (Volume 2) under heat rejection
equipment and see if this equipment piece will connect to a WLHP...sometime
there are little details that DOE-2 won't let happen exactly as you want it.
Hope this helps you a little.
Pasha
On Mon, Sep 17, 2012 at 9:24 AM, Miller, Jessica <JMiller at trojb.com> wrote:
> I am trying to attach a heat-rejection fluid-cooler to a WLHP
> circulation-loop but my simulation keeps crashing out at 18% and I get an
> error:****
>
> ** **
>
> Loop: FC Water Loop CL 1 has zero design flow. Check input for
> consistency, or specify design loads. Does anyone know what I might be
> doing wrong?****
>
> ** **
>
> Thank you!****
>
> ** **
>
> ** **
>
> I set the following properties:****
>
> ** **
>
> "FC Loop Pump 1 CL" = PUMP ****
>
> ..****
>
> ** **
>
> "CL Grnd Loop 1" = CIRCULATION-LOOP****
>
> TYPE = LAKE/WELL****
>
> LOOP-DESIGN-DT = 10****
>
> MIN-RESET-T = 65****
>
> ..****
>
> ** **
>
> "FC Water Loop CL 1" = CIRCULATION-LOOP****
>
> TYPE = WLHP****
>
> SUBTYPE = SECONDARY****
>
> PRIMARY-LOOP = "CL Grnd Loop 1"****
>
> LOOP-OPERATION = STANDBY****
>
> DESIGN-HEAT-T = 70****
>
> DESIGN-COOL-T = 85****
>
> COOL-SETPT-CTRL = FIXED****
>
> LOOP-PUMP = "FC Loop Pump 1 CL"****
>
> ..****
>
> ** **
>
> SET-DEFAULT FOR HEAT-REJECTION ****
>
> TYPE = FLUID-COOLER****
>
> CAPACITY = 1.2863e+006****
>
> NUMBER-OF-CELLS = 1****
>
> CAPACITY-CTRL = VARIABLE-SPEED-FAN****
>
> COIL-LOSS = 252900****
>
> DESIGN-APPROACH = 7****
>
> DESIGN-WETBULB = 78****
>
> CW-STATIC-HEAD = 0****
>
> CW-FLOW-CTRL = VARIABLE-FLOW****
>
> SPRAY-KW/CELL = 2.2371****
>
> ..****
>
> ** **
>
> "WLHP Fluid Cooler 1" = HEAT-REJECTION ****
>
> TYPE = FLUID-COOLER****
>
> CW-LOOP = "FC Water Loop CL 1"****
>
> ..****
>
> ** **
>
> *Jessica K. Miller, EIT, LEED® AP*****
>
> Associate****
>
> HVAC Engineering****
>
>
> *TRO Jung|Brannen
> *22 Boston Wharf Road
> Boston, Massachusetts 02210
>
> *t* 617.502.3400
> *f* 617.502.3401
>
> *www.trojungbrannen.com*****
>
> ** **
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120919/f3c3c281/attachment-0002.htm>
More information about the Equest-users
mailing list