Nimesh,

Are you trying to apply ASHRAE 90.1 for a building in Singapore?  I think you should check 
first the commercial building energy standard in Singapore, instead.  However, if  you do 
want to do a simulation in accordance to the ECB method in ASHRAE 90.1, the Reference 
Building should be architecturally the same as your Proposed Building, but with shell 
conditions as prescribed in the standard for the appropriate Climate Zone, which for 
Singapore must be Climate Zone 1.  For more information on ASHRAE 90.1 modeling rules, 
please look at the ECB chapter (Chapter 11 in the 2004 version, my latest) of the standard.

Joe

Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
yjhuang at whiteboxtechnologies.com
www.whiteboxtechnologies.com
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"


On 9/20/2012 7:40 PM, Nimesh Prajapati Nimesh wrote:
> Dear Friends,
>
> I am confused here: What is Baseline Standard for Singapore Buildings using which I can 
> create Baseline model?
>
> Shall I use ASHRAE 90.1 Appendix - G? Can anybody guide me?
> Thanks,
>
> Nimesh Prajapati
>
> HVAC Design Engineer
> (+91 9687133492)
> email: nimonomics at yahoo.in
> Skype: nimonicideas
> Please consider the environment before printing this e-mail.
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120920/3c62f7d9/attachment-0002.htm>


More information about the Equest-users mailing list