Need to review some of your inputs.  The HW loop is set to STANDBY which
means the pump will run whenever a system fan is scheduled on and the
system's heating is available.  Looking at your input, the HW loop is
always on as system fans are on 24/7 and heating is always available.  The
PMZS units have gas furnaces with the cold deck control = RESET.  The
default hot deck control is CONSTANT at 120F as input.  PMZS has a default
minimum hot deck airflow of 1%.  Each of these units is 100% outside air
24/7.

On Tue, Sep 25, 2012 at 2:51 PM, Michael Campbell <
mike at sustainablesolutionscorporation.com> wrote:

> Hello,
>
>
>
> I have an issue for my proposed design for my LEED model.  It ends up
> using a significant amount of gas for heating during the summer.  However,
> the baseline model is not using gas for heat during the summer.  Does
> anyone have an idea for why this might be?
>
>
>
> Thanks,
>
>
>
> *Mike Campbell, EIT, LEED AP O+M
> Sustainability Specialist*
>
> (610) 569-1047 office
>
> (610) 569-1040 fax
>
> mike at sustainablesolutionscorporation.com
>
> www.SustainableSolutionsCorporation.com<http://www.sustainablesolutionscorporation.com/>
>
>
>
> [image: Description: cid:image002.jpg at 01C81E05.97C02180]
>
>
>
> [image: Description: WBE_cmyk_CP copy] [image: Description:
> E_BCorp_logo_POS]
>
>
>
> *This email message and any attachments are for the sole use of the
> intended recipient(s) and may contain confidential and privileged
> information. Any unauthorized review, use, disclosure or distribution is
> prohibited. If you are not the intended recipient, please contact the
> sender by reply email and destroy all copies of the original message and
> any attachments.*
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>


-- 
Ron Pecarina, PE, CEM, LEED-AP BD&C
Energy and Sustainable Design Consultants, Inc.
1128 Noblewood Drive
Billings, MT   59101
406-208-0227
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120925/29b223e3/attachment-0002.htm>


More information about the Equest-users mailing list