[Equest-users] Condensate Capture
Hall, Brendan
BHall at karpinskieng.com
Wed Sep 26 10:33:09 PDT 2012
I would create an hourly report for whatever air handler(s) serving your condensate collection system and select the system air flow, mixed air humidity ratio, and humidity ratio of air leaving cooling coil and go from there. You may want to also grab the density of the air at coil, but that won't vary greatly. However, if you are at altitude you will want to correct for that. Export the hourly results into excel and you should be able to calculate a reasonable estimate of the amount of water removed from the airstream. Keep in mind that you are likely using the weather for an average year (TMY2 file) , so your mileage will vary.
Brendan Hall, M.Sc., LEED AP BD+C
Engineer, Mechanical
karpinski
ENGINEERING
3135 Euclid Avenue
Cleveland, OH 44115
P 216.391.3700 x 3111
E bhall at karpinskieng.com<mailto:bhall at karpinskieng.com>
W www.karpinskieng.com<http://www.karpinskieng.com/>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Pasgar, Arash
Sent: Wednesday, September 26, 2012 12:59 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Condensate Capture
Hi,
How can I find the amount of mechanical units condensate drain (gallon per day) in equest?
Because, it is going to use for irrigation and architect need it for landscaping credit.
Thanks for your help
Arash Pasgar
Mechanical Designer
[Description: Description: Description: Description: Description: Description: image001]
v. 210.546.0200 | www.dbrinc.com<http://www.dbrinc.com>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120926/6831ab16/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 4870 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120926/6831ab16/attachment-0002.jpg>
More information about the Equest-users
mailing list