[Equest-users] eQuest modeling of Open / Uncovered Staircases
nimesh.prajapati
nimesh.prajapati at hitechcaddservices.com
Sat Sep 29 02:12:24 PDT 2012
Dear Nick,
Thank you very much.
Thanks,
Nimesh Prajapati
(+91 9687133492)
HVAC Design Engineer & Energy Modeller
Description: Description: C:\Users\nimesh.prajapati\Desktop\CADD.jpg
P Please consider the environment before printing this e-mail
From: Nick Caton [mailto:ncaton at smithboucher.com]
Sent: 27 September 2012 23:02
To: nimesh.prajapati; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] eQuest modeling of Open / Uncovered Staircases
Hi Nimesh,
Looks like my first guess was correct - I'll stand by my suggestions to not
include those stairs as part of the envelope perimeter, model the exterior
doors for each level. At your option, the shading effect of the stairway
constructions upon the envelope to reduce solar gains could be incorporated
via building shades in detailed mode.
If there are any stairwell lighting loads for consideration, I'd make a
point to handle those alongside perimeter/exterior area lighting with
appropriate scheduling.
Best of luck!
~Nick
cid:489575314 at 22072009-0ABB
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: nimesh.prajapati [mailto:nimesh.prajapati at hitechcaddservices.com]
Sent: Wednesday, September 26, 2012 11:21 PM
To: Nick Caton; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] eQuest modeling of Open / Uncovered Staircases
Dear Nick,
I am attaching herewith the building layout for the building showing the
staircases. Note that the as per the building layout these staircases are
not covered and open to surroundings.
There is no HVAC System serving to these staircases.
Thanks,
Nimesh Prajapati
(+91 9687133492)
HVAC Design Engineer & Energy Modeller
Description: Description: C:\Users\nimesh.prajapati\Desktop\CADD.jpg
P Please consider the environment before printing this e-mail
From: Nick Caton [mailto:ncaton at smithboucher.com]
Sent: 22 September 2012 00:58
To: Nimesh Prajapati Nimesh; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] eQuest modeling of Open / Uncovered Staircases
Hi Nimesh,
If I'm correctly guessing the stairs are exterior to the building perimeter,
I would advise not wrapping your envelope around the stairs and creating
false interior spaces. Do model the exterior doorways, and consider
approximating their effect as building shades for your proposed model (not
the baseline).
If you're asking about open interior staircases interconnecting three
stories, and your question is more about thermal zones/system relationships,
I think the mailing list needs more info on those things to provide an
informed response.
~Nick
cid:489575314 at 22072009-0ABB
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nimesh
Prajapati Nimesh
Sent: Thursday, September 20, 2012 9:37 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] eQuest modeling of Open / Uncovered Staircases
Dear Friends,
In one my recent Project I have building which is having five nos of Open /
Uncovered Staircases and the building is three storey.
Shall I consider as part of building envelope and model it in eQuest for
Baseline & Proposed Case?
Can anyone guide me?
Thanks,
Nimesh Prajapati
HVAC Design Engineer
(+91 9687133492)
email: nimonomics at yahoo.in
Skype: nimonicideas
Please consider the environment before printing this e-mail.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120929/4f95b672/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2833 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120929/4f95b672/attachment-0006.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120929/4f95b672/attachment-0007.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2833 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120929/4f95b672/attachment-0008.jpeg>
More information about the Equest-users
mailing list