[Equest-users] Effect of reflectivity on building energy consumption
RobertWichert
robert at wichert.org
Sat Sep 29 07:51:54 PDT 2012
Dear Nimesh Prajapati,
It looks like your gas consumption went DOWN with increased
absorptivity. This makes sense to me since the building will absorb
more solar heat and keep itself warm.
It looks like your electric consumption went UP with increased
absorptivity. This also makes sense since the building heat loads are
increased by the additional solar heat.
Am I getting this correct?
Robert Wichert P.Eng. LEED AP BD&C
+1 916 966 9060
FAX +1 916 966 9068
===============================================
On 9/29/2012 2:37 AM, nimesh.prajapati wrote:
>
> Dear Friends,
>
> I have typical case study and friendly saying I don't know whether I
> am in correct direction or not, so requesting you to please guide me.
>
> I am trying to analyse effect of reflectivity on building energy
> consumption. What I had done is as per followings:
>
> 1.For simple room created in eQuest I had kept all other parameters same.
>
> 2.I had taken three case study (Case-01, Case-02, Case-03 ) by
> changing the parameters as mentioned in the attached sheet. (Changed
> parameters are marked as blue)
>
> 3.Then I have the output results as attached in the sheet.
>
> 4.Results shows that as absorptivity increases there is saving in
> cooling but heating have reverse effect.
>
> Can anybody help me out? I am trying on myself and will like to have
> guidance from you friends.
>
> Thanks,
>
> Nimesh Prajapati
>
> (+91 9687133492)
>
> HVAC Design Engineer & Energy Modeller
>
> Description: Description: C:\Users\nimesh.prajapati\Desktop\CADD.jpg
>
> PPlease consider the environment before printing this e-mail
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120929/7503f0ca/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2840 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120929/7503f0ca/attachment-0002.jpeg>
More information about the Equest-users
mailing list