Hi All,
Does anyone know how to create DOE 2.2 formulas to have Equest calculate
outside air accordingly? I am typically modeling multi-family projects. As
such my models all have MANY single zone split systems (over 400). Per
ASHRAE 62.1, Outside Air = OA-FLOW/PER * NUMBER-OF-PEOPLE + OA-FLOW/AREA *
AREA. However equest only uses the larger of OA-FLOW/PER * NUMBER-OF-PEOPLE
or OA-FLOW/AREA * AREA. I have tried to create a formula and input it into
the field OUTSIDE-AIR-FLOW but I am not very familiar with DOE 2.2 syntax.
AREA is a SPACE property. NUMBER-OF-PEOPLE is a SPACE property.
OUTSIDE-AIR-FLOW, OA-FLOW/PER and OA-FLOW/AREA are all ZONE properties.
How would I write a ZONE formula for OUTSIDE-AIR-FLOW that calls the
corresponding SPACE values for AREA and NUMBER-OF-PEOPLE? I am sure it has
to do with Parent/Child relationships in Equest/DOE 2.2. Is the Space the
parent or child of the zone? Is the space a parent or child of the polygon?
= #L("OA-FLOW/PER")* ?? + #L("OA-FLOW/AREA")*??