[Equest-users] Cooling/Heating Capacity Ratios - LEED Report?
Nick Caton
ncaton at smithboucher.com
Wed Apr 10 13:04:29 PDT 2013
Hi folks,
I have a seemingly simple LEED comment which has been causing me to chase my tail this afternoon. I feel like this should be really easy to document in a crystal-clear fashion, but I must be missing something:
The Task:
Document with clarity that the baseline system cooling and heating capacities are using the 1.15 and 1.25 (respectively) capacity sizing ratios as prescribed in 90.1 Appendix G.
Intuitively, I have a sense we should be able to simply and directly reference one or a series of the *.SIM reports to substantiate the systems are oversized by the appropriate factors. After spending some time digging through the reports and associated help documentation however, I'm empty-handed and do not think the actual ratio inputs (COOL-SIZING-RATI / HEAT-SIZING-RATI) are reported.
Further, I tried deriving the oversizing ratio between a system's annual PEAK (re: report SS-P) and calculated system capacity (report SV-A) as reported... but the math doesn't quite work out! It's the right ballpark, but I don't think I can write the difference off as a rounding error...
The Solution(?):
For now, I can just provide screen grabs illustrating the inputs in eQuest's spreadsheet view with relative ease, but if this is possible to document by assembling/referencing one or more additional reports for future models I'd prefer to adopt that in practice and avoid the same question down the road. If I have some misunderstanding or new nuance to learn about the reports that would be worthwhile as well =).
Any suggestions/experience?
Thanks in advance!
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130410/ba2d6a7e/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130410/ba2d6a7e/attachment.jpg>
More information about the Equest-users
mailing list